overheating neutral link

Joined
16 Feb 2011
Messages
10,770
Reaction score
1,804
Location
Sheffield
Country
United Kingdom
hi any advise would be helpfull. just looked at a mates fuseboard because he could smell burning everything looked ok untill i spotted the main neutral link bar from the main switch which links the two rcd split loads looked overheated have checked and it seems tight, this only happens when they use the shower 9.5-8.3 kw via a 40amp mcb
 
Sponsored Links
What's the cable from the CU to the shower? If it's a 6mm and a longish cable run that could well come under stress from a 9kw shower, but the 40A MCB is slightly too big for the cable.

PJ
 
Sponsored Links
Have you checked "neutral link bar" is actually in U clamp under main switch as have seen a few where it is not in the clamp and just touching?

Also does main switch feel "gritty" when operated as some times a lack of care during install can lead to crud in switch contacts?

sorry if this is teaching you to suck eggs ;)
 
hi main switch feels fine the neutral seems to be overheating where it connects to the strip at the top of the consumer unit and splits off to feed the two rcd's this is where i find it strange can understand if it was getting hot at the fuse input ? thanks for the input
 
Sparkymarka "thinks its a 6mm cable." Would it be wise to confirm this? ie. if the cable csa is too small this could cause the smell?
 