Today i was doing a pir for a client after visually inspecting parts of the house it became apparent that a 6mm old cooker cable had been used to supply a ring main wired in 2.5 to the kitchen. Obviously it had been terminated in a jb some where as there was no evidence of a 6mm cable to any of the kitchen sockets.
I tested out the small ring and it was complete, to determine the r1+r2 of the radial/ring i found mid socket of the ring and shorted live to earth and tested the result was 0.12ohms zs at socket was 0.78 ohms my question is have i done this correctly as it is the first time i've came across this situation?,i don't like doing periodics full stop. been a FULLY qualified sparks for 19 years every day is a school day! thanks in advance.
I tested out the small ring and it was complete, to determine the r1+r2 of the radial/ring i found mid socket of the ring and shorted live to earth and tested the result was 0.12ohms zs at socket was 0.78 ohms my question is have i done this correctly as it is the first time i've came across this situation?,i don't like doing periodics full stop. been a FULLY qualified sparks for 19 years every day is a school day! thanks in advance.