OK forget what BS7671 says, let us look at the real problem in using a lighting circuit, and that is a fault can cause us to lose the lights, so back in the day of fuses in the distribution unit using the smallest fuse that will fit a fused connection unit that is 1 amp, we could be reasonable sure a fault would blow a fuse rather than cause loss of lights.
Today that is not the case, it takes 30 amp to trip a MCB in the 0.01 seconds and well over that to rupture a 1 amp fuse, and the getting into the loft to disconnect what ever has caused it to blow likely means dropping loft ladders which likely needs doing in the dark.
However fitting the FCU so it can be switched without going into the loft would mean the fault could be removed without access to loft, so as long as the switch on a switched FCU is accessible without the use of steps or ladders, then the rise is to my mind within acceptable limits. The other option is to ensure there is still enough light after the lights fail, last house had a emergency light top of stairs so any power cut there was enough light to safely get to the garage where the consumer unit was located.
So now returning to BS7671, it states
Today that is not the case, it takes 30 amp to trip a MCB in the 0.01 seconds and well over that to rupture a 1 amp fuse, and the getting into the loft to disconnect what ever has caused it to blow likely means dropping loft ladders which likely needs doing in the dark.
However fitting the FCU so it can be switched without going into the loft would mean the fault could be removed without access to loft, so as long as the switch on a switched FCU is accessible without the use of steps or ladders, then the rise is to my mind within acceptable limits. The other option is to ensure there is still enough light after the lights fail, last house had a emergency light top of stairs so any power cut there was enough light to safely get to the garage where the consumer unit was located.
So now returning to BS7671, it states
so fitting emergency lights removes the danger, so as long as emergency lights fitted, then there is really no problem fitting a 13A socket on a lighting circuit.Every installation shall be divided into circuits, as necessary, to take account of danger that may arise from the failure of a single circuit such as a lighting circuit.