Hi all
If anyone has anything ideas about this i'd be grateful, before I spend out more money... thanks.
For almost 8 months I've had a intermittant problem with my central heating (potterton suprima 30 and boilermate II) as almost everyday the potterton has gone into lockout (red flashing light) and must be reset. After two plumbers replaced the overheat stat, ignition lead and electrode, pump and de-gunged the system I finally diagnosed the themostat on the boilermate as faulty, thus constantly requesting heat. The potterton has been firing every five minutes or so and switching itself off when it hits the temperature regulated by its own thermostat. The potterton eventually locks out and then there is no hot water for a shower the next day etc.
Having stood next to it when it shut down recently I measured the temperature of the flow pipe (the pipe taking the hot water back to the tank) to be about 70Celsius - so the lockout is not an overheating problem (the potterton will overheat at 90 i understand).
I pressed reset a few seconds after the boiler when off and it locked out again. I repeated this about 5 times and noticed that the potterton locks out at the moment when the green light is flashing rapidly (ie ignition). Looking through the window shows that the sparks are there but the ignition fails. the fan blows, the sparks spark but the gas does not light every time.
waiting 20 minutes or more the reset button fired up the boiler again and everything went back to normal.
I've this week replaced the thermostat on the boilermate and so this lockout problem is much less frequent now. To be clear, most of the time the potterton seems to work fine.Since the boilermate is not constantly requesting heat the boiler fires much less frequently and so this ignition problem occurs less frequently too (once in three days). However there is still a problem and I would like to sort it out. The plumber has suggested that it could be a sticky gas valve, or the PCB on the potterton or a sticky governor (external to the house I understand).
Can anyone think of any other causes and any way to sucessfully diagnose which of the possibilities it is?
thanks in advance
Andy
If anyone has anything ideas about this i'd be grateful, before I spend out more money... thanks.
For almost 8 months I've had a intermittant problem with my central heating (potterton suprima 30 and boilermate II) as almost everyday the potterton has gone into lockout (red flashing light) and must be reset. After two plumbers replaced the overheat stat, ignition lead and electrode, pump and de-gunged the system I finally diagnosed the themostat on the boilermate as faulty, thus constantly requesting heat. The potterton has been firing every five minutes or so and switching itself off when it hits the temperature regulated by its own thermostat. The potterton eventually locks out and then there is no hot water for a shower the next day etc.
Having stood next to it when it shut down recently I measured the temperature of the flow pipe (the pipe taking the hot water back to the tank) to be about 70Celsius - so the lockout is not an overheating problem (the potterton will overheat at 90 i understand).
I pressed reset a few seconds after the boiler when off and it locked out again. I repeated this about 5 times and noticed that the potterton locks out at the moment when the green light is flashing rapidly (ie ignition). Looking through the window shows that the sparks are there but the ignition fails. the fan blows, the sparks spark but the gas does not light every time.
waiting 20 minutes or more the reset button fired up the boiler again and everything went back to normal.
I've this week replaced the thermostat on the boilermate and so this lockout problem is much less frequent now. To be clear, most of the time the potterton seems to work fine.Since the boilermate is not constantly requesting heat the boiler fires much less frequently and so this ignition problem occurs less frequently too (once in three days). However there is still a problem and I would like to sort it out. The plumber has suggested that it could be a sticky gas valve, or the PCB on the potterton or a sticky governor (external to the house I understand).
Can anyone think of any other causes and any way to sucessfully diagnose which of the possibilities it is?
thanks in advance
Andy