Does the current numbering have any logic to it? I couldn't make any sense of it.You can buy new stickers or just make your own and number them however you want.
Does the current numbering have any logic to it? I couldn't make any sense of it.You can buy new stickers or just make your own and number them however you want.
Can you elaborate on this please. I think this is the corresponding image:The brown in Mcb 1 looks like it has a tight loop in it, that should be avoided
and some more info on this please. I think this is the corresponding image.and your technique for stripping the sheath in the sockets needs slight improvement
Likely using stock from pre rcd boards that took all mcbs maybe 13Does the current numbering have any logic to it? I couldn't make any sense of it.
Quite the opposite. I think they should be right to left like the neutrals and MCBs.Does the current numbering have any logic to it? I couldn't make any sense of it.
Have you been photographing one of my CUs?You don't want to end up like this.
You could be right, but I don't think so. 'kinky' I think there's just a bit of the upgoing brown which goes up and down in front of the G/Y - i.e. if one pulled it down slightly (towards the MCB), it would be clear that it all went behind the G/Y .....1, maybe an illusion but the brown in mcb one looks like it loops round the earth.
I have 10 usable ways and the earth bar goes up to 13. Which MCB should I treat as 1 on the earth bar?I would just (probably just 'mentally') count/number all of the devices which supply circuits (i.e. MCBs/RCBOs, not RCDs or Main Switch) from left to right, and then use the corresponding earth bar terminals with the corresponding numbers.
I really don't think it is of all that much importance but, as I said, since (unlike those on the neutral bars) the numbers on the earth bar go from left to right, I would use #1 on the earth bar for the left-most MCB, and then 'work to the right' from there with the numbering (for both earth bar and MCBs).I have 10 usable ways and the earth bar goes up to 13. Which MCB should I treat as 1 on the earth bar?
Essentially yes and yes. You would then also probably have to shorten the busbar currently fed by the RH RCD.To add an RCBO into this unit, do I move the right RCD along one to create space for the RCBO?
Does it then need its own busbar connecting to main switch? I assume it shouldn’t be sharing busbar with the current block of RCD and MCB’s..
Others will undoubtedly disagree with me here but, for what it's worth, as I've often reported, my personal experience is that if I tighten the terminal screws of devices within CUs (MCBs, RCBOs, Main Switches etc.) with either of my two torque screwdrivers (one was a gift!) to the "manufacturer's recommended torque", I am frightened by how 'loose' they end up - but maybe others don't have that experience.One more for you guys, do folks always use a torque screwdriver when working on a CU?
I’ve got a set of Stanley Fatmax VDE Screwdrivers that serve all my electrical needs and loathed to go out and purchase a torque driver. Interested to hear your experiences.
Am I limited to a maximum of 5 RCBO’s on this CU or can I get rid of the first RCD and have 7 RCBO’s? If yes, can the N for two of these RCBO’s spill over to the second N terminal bar?Essentially yes and yes. You would then also probably have to shorten the busbar currently fed by the RH RCD.
Kind Regards, John
If, as well as getting rid of the RH RCD, you moved the LH RCD to the left (and shortened its busbar), you could (by adding an appropriate long busbar) presumably have 9 RCBOs.Am I limited to a maximum of 5 RCBO’s on this CU or can I get rid of the first RCD and have 7 RCBO’s?
The phrase "spill over" is a little worrying (see below) but, yes, if you got rid of the RH RCD you could then link (connect) together the two right-hand neutral bars (with a short bit of cable) (effectively producing a longer bar) and then use all the remaining holes in both of the bars for the (however many) RCBO circuits. Indeed, if you got rid of both RCDs, you could presumably have 14 RCBOs, and link together all three neutral bars for their circuits.If yes, can the N for two of these RCBO’s spill over to the second N terminal bar?