I have attached a picture, This shows the opening we have for the stairway and directly above is where the truss meets the floor, You can see from this angle however that the truss is connected to the binder and not a supporting wall underneath which is the same for all 4 trusses, So my point in making supports within the new loft area as per my diagram above going direct down to the binders is where I plan to put the new supports we want to put them directly over the internal walls fopr extra support so why is that not better than what is their at the moment?
I can see dowels into the binders, and I would imagine that there is also a connection from the truss to the existing ceiling joist.
What you will find is that the truss isn't being supported by the binder, but is actually supporting it, due to the effect of triangulation. The binder will in turn give further support to the ceiling joists.
So you won't be able to transfer load to the binder once the truss is gone.
The other thing I've noticed is that it's not just the top purlins which are given support by the trusses, but the bottom ones too. Remove the trusses, and the lower purlins sag, imposing load to the new steelwork...but the steels are at maximum capacity already, so you can't allow that to happen...
You need to get support to all four purlins, once the trusses are removed, and that involves more steelwork. One option would be to splice through the steels already in place with more steels (at 90 degrees to them), and send props up to the purlins.
Your SE has cocked up, pure and simple...