When I achieved a situation in which all final circuits in my house’s (TT) installation were explicitly protected by RCDs or RCBOs, my initial thought was that the up-front Type S RCDs had become essentially redundant. Neverthelss, I retained them, not the least because they served as useful isolators (and appeared to do no harm, other than the very small risk that they would take out a whole phase if there was a N-E fault on one of the couple of final circuits protected by SP RCBOs).
However, on reflection, I think that those up-front RCDs probably are still required, to protect the (several) sub-mains. 411.3.2.4 requires that a distribution circuit in a TT installation has an L-E fault disconnection time not exceeding 1 second. Certainly if I had anything approaching a ‘pure TT’ installation, there’s obviously no way that such a disconnection time (indeed, any disconnection at all!) could be achieved by the 60A/80A fuse protecting the sub-main – so, it seems to me that I still do need those RCDs. Do people agree?
In practice, ‘incidental paths to earth’ in my TT installation are currently such that EFLI is very low, probably low enough for the sub-main fuses to provide the <1 disconnection time. However, it doesn’t feel right that I should rely on that, since a man from the water supplier with a bit of plastic pipe could change the situation dramatically ‘overnight’. Again, do people agree?
Kind Regards, John
However, on reflection, I think that those up-front RCDs probably are still required, to protect the (several) sub-mains. 411.3.2.4 requires that a distribution circuit in a TT installation has an L-E fault disconnection time not exceeding 1 second. Certainly if I had anything approaching a ‘pure TT’ installation, there’s obviously no way that such a disconnection time (indeed, any disconnection at all!) could be achieved by the 60A/80A fuse protecting the sub-main – so, it seems to me that I still do need those RCDs. Do people agree?
In practice, ‘incidental paths to earth’ in my TT installation are currently such that EFLI is very low, probably low enough for the sub-main fuses to provide the <1 disconnection time. However, it doesn’t feel right that I should rely on that, since a man from the water supplier with a bit of plastic pipe could change the situation dramatically ‘overnight’. Again, do people agree?
Kind Regards, John