For many, a UPS on the boiler would be sufficient to keep it running - the load isn't all that much.
Do you mean to run a combi to the extent of being able to heat water? If so, you're probably right. As for pumped CH systems, uinless it were a pretty massive UPS, I wouldn't think it would run the pump(s) for very long at all, would it?
Well it depends on "a lot" I suppose. The manual for our boilers states 150W, a
UPS we've sold a few of at work has a nominal runtime of 116 minutes at 150W load.
So you could run the system continuously for a while, then run the genny for a bit, rinse and repeat. Or, you could just run the heating for 5 minutes every 15 or so - warm the rads up and then turn the heating off. Better than no heating at all !
But it's not about how massive the UPS is, it's about how much battery capacity it has.
But I too have a petrol genny (3kVA) if needed
I know from experience (used it at work a few times - keeps the petrol fresh(er)) it'll run 2kW of IT gear - though it struggles when the UPS tries to recharge it's batteries at the same time.
If the equipment itself is using most of the available power, I suppose that makes sense - but I wouldn't think that the charging of (modest sized) UPS batteries would, per se, represent much of a demand on the LV supply.
Part of the problem is that when you've 2kW of load, and the UPS dumps it onto the genny, then the genny output droops - that was the first problem we had and needed to change settings on the UPS to be less sensitive to mains voltage fluctuations. Then, if the load has been on battery for a while, the UPS can take a fair bit extra (I've seen as much as 50% of it's rating during testing on a couple of larger units) for charging batteries - 2kW + 50% is going to fully load a 3kVA genny. I haven't actually tested, but I think most of the models I've worked with fire up the charger immediately the mains comes back - so the genny has to instantly pick up as much as 150% of the supplied load.
So it can be worth shedding a bit of load (turn off a server or 2), transferring to genny, letting the batteries recharge for a few minutes (the charge current soon drops off), and then adding the loads back.
While we'll we're getting somewhat off topic, most of the UPS manufacturers recommend massively oversized gennys. Ie, if you have (say) a 3kVA UPS, they'll suggest anything up to 10kVA as a minimum genny rating to feed it ! Though to be fair, the genny manufacturers say the same - for the reasons I've described, it can be "tricky" getting an IT load started up/transferred to a genny that's not got a good bit larger than the load.
They also similarly overspec the minimum mains supply needed.
At work we have a supply with 63A fuse by the meter. As a result, that means we have to consider not just our normal load, but also the result of recovering from a power cut - it would be "a bit annoying" if we managed to survive a power cut, only to blow the supply fuse shortly after the power comes back on.
Discussions with manufacturers regarding the possibility of limiting charging current to keep within supply limits, or to take the charger supply from a separate input, gets the response "wrong supply" - usually adding "and we won't provide any support if you don't follow that recommendation". For the 16kVA unit we have, they state a minimum of 100A supply regardless of configuration or actual load - we currently have 7kW of load, on a unit with 12vKA of power modules installed.