As it happens, a Chinese inch (A cun), is 1.3123 in.Chinese volts and amps might be different to European volts and amps too.
As it happens, a Chinese inch (A cun), is 1.3123 in.Chinese volts and amps might be different to European volts and amps too.
The manual is here: https://midsummerwholesale.co.uk/pdfs/en-k-manual-v1.4.pdf
appears that the 13mm size refers to the outer diameter of the round cable that can be used with the AC connection plug but has been jumbled up with other information. Page 17 onwards.
A 100A breaker will be of no use - plenty of homes have an incoming supply smaller than that.
If that flat cable has been shoehorned into the inverter connection plug, it's the wrong type.
May not be secured properly.
Round cable is required.
Could you post a photo of your CU?
Don't quote me on what I think cables do or go exactly where, unsure of that but here's a photo of the cables. Both dc coming from pv and to cu. This what you would expect?7kW @ 240V is 29.2 Amps so 32A RCBO and 4mm² cable.
Did you decide what size cable yours is?
Mind you, I don't recall having herd of many people called "Clatter"Chinese volts and amps might be different to European volts and amps too.
Mr Hill (Benny) claimed that a child was named at what we might refer to as the Christening Party, they`d eat the meal, wipe the cutlery then throw it high into the air and the sound it made when hitting the table/floor as it landed is what they called the child.
Sounds more like plumbing than wiringThanks, so this uk version says the breaker should be 80a for our install with battery. Still a lot bigger than the 32a that was used. ....
, its grey cable, its width longer than its height. How can I identify what gauge cable they've actually used?
Electrics:flatpvccables
www.diynot.com
You don't want minimal cable sizings with PV.7kW @ 240V is 29.2 Amps so 32A RCBO and 4mm² cable.
Did you decide what size cable yours is?
Maybe that's why they are asking for a cable with a 22mm outside diameterYou don't want minimal cable sizings with PV.
I'm not for a minute defending the demands made by the manufacturer!Maybe that's why they are asking for a cable with a 22mm outside diameter
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local