What would be the maximum safe load for a single 5 Meter run of 2.5mm2 T&E PVC cable clipped direct to an internal brick wall?
 
Sponsored Links
BlueIce said:
What would be the maximum safe load for a single 5 Meter run of 2.5mm2 T&E PVC cable clipped direct to an internal brick wall?
2.5MM has a max capacity of 27A. altho it would have to be on a 20A MCB
 
Although some manufacturers do produce 25amp MCB's. These could be used for a fixed appliance.

What are you trying to achieve??
 
Thanks to you both for the information!


2.5MM has a max capacity of 27A. altho it would have to be on a 20A MCB

Would that be 27A CONTINUOUS max load at 240V?
 
Sponsored Links
BlueIce said:
Thanks to you both for the information!


2.5MM has a max capacity of 27A. altho it would have to be on a 20A MCB

Would that be 27A CONTINUOUS max load at 240V?

yes, and technically, its 230V. and running at 27A, it will be hot and possibly as high as 70 deg C
 
BlueIce said:
Thanks to you both for the information!


2.5MM has a max capacity of 27A. altho it would have to be on a 20A MCB

Would that be 27A CONTINUOUS max load at 240V?

27A continuous clipped direct to a non metalic surface (or embedded in building material in line with method 1) with a 30 deg centigrade ambient temperature, not grouped with other cables and not run through thermal insulation. 240v does not have a bearing on the current carrying capacity of a cable, it is 27A wether it is 240v, 110v or 12v.
 
BlueIce said:
Thanks to you both for the information!
Would that be 27A CONTINUOUS max load at 240V?

Yes, but thats clipped direct rating without any correction factors applied, unlikely to occur in a house, best to assume 20A as a rough guide*in the average way its installed in a house, any more than this I'd use 4mm²

*Rough guide only, exact installtion method, derating factors, volt drop, disconnect time, etc need to be all calculated and taken into account when selecting a cable

Useul table here: http://www.tlc-direct.co.uk/Figures/Tab4.7.htm
 
Adam
Could you explain the calculation for voltage drop on the table please.
e.g. 2 core 1.0mm cable voltage drop 44.0 amps/metre?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top