Hi John,
Most mainstream manufacturers still publish their output tables as dT50 for continuity and because it is a BS standard, some, particularly those who may be aiming at the renewables market, will also publish lower dT tables for the convenience of the informed customer. It is up to the system designer to understand the basis of the specs to which equipment is sold and to apply 'corrective' factors as appropriate.
The reality of what is actually done - it depends entirely on the level of skills, knowledge and drivers of those involved, there is no effective mechanism for enforcing regulations.
The unfortunate truth is that many of the trades persons who find a career in the domestic heating industry are from the pool of school leavers who are less academically able and who learn best by example from their colleagues, the result being that outdated practises are handed on for extended periods. Additionally if one is not academic, being presented with a whole bunch of calculations is daunting at best.
The result is failure to apply best practice more often than not,
much of what we have discussed here will be of little interest to many trades and certainly not applied. There is NO policing/enforcement so the status quo endures,
So to answer your question bluntly - proper design is routinely not done because the installer is unwilling, unaware, unable to undertake it. This is a totally different thing to being good at the physical act of installing and is a completely different subject to gas safety!
I would agree with you that triple panel rads are not a domestically acceptable solution, there are others, UFH is great but only really financially sensible at (re)build, fan assisted rads are now available in domestic formats and can almost double the output of a rad, skirting heating can sometimes be a solution and can help alleviate those pesky convection drafts.
All of the solutions are more expensive than the mass produced steel panel rad and this is a major part of the barrier to installation of low temp systems, a fight which the government seems to expect the installer community to take up for them!
If you are attempting to size your new system then one strategy you might adopt to achieve realistic financial and physical size whilst ensuring best performance/efficiency is:
Make your heat loss calculations for steady state losses on 'design day conditions' ie the coldest conditions you intend the system to cope with. (typical industry standards are -3 to -5 depending on region)
Determine the radiators that will supply those heat requirements based on the dT50 tables.
Establish which room is most physically constrained size wise and decide what is the largest affordable radiator that will fit in that room eg. 120% larger than the dT50 tables would lead you to choose.
Reselect ALL the rads to be 120% larger than the original selection.
Establish, using the dT correction factors, what average rad temperature will give the 'design day output' and the design boiler flow will be this plus 10C.
Hopefully this will give some useful reduction in boiler flow temperature, the lower the better in terms of boiler efficiency.
Also it will give you a margin for heating startup if you elect to operate the heating discontinuously eg. programming it off while out to work
Some asides to consider - design day temperatures do not need to be the lowest temp that you would ever expect to see weatherwise, the coldest days are but a few a year and on those days it may be more practical to supplement the CH with secondary sources (gas fire, wood stove, electric heater) and/or extra clothing, doing so will give you a CH system that will operate that much more efficiently the other 98% of the year.
Having fitted the system that will do the job for the acceptable worst conditions of the year, it is worth considering that almost the entirety of the year will require significantly less output than a 'design day'
The flow temperature you operate the boiler at is not fixed in stone just because of the figures used at design.
During warmer spring and autumn days the boiler can be operated at lower flow temperatures and still achieve the required heat output from the rads to make good the lower heat losses from the building.
The simplest way is to manually adjust the boiler stat based on the weather forecast or just a seasonal expectation very easy particularly on a combo where you do not have to consider a minimum boiler flow temp to achieve DHW.
On stored hot water systems or where you wish to track this method of operation tightly to the actual weather many manufacturers offer 'Weather Compensating' controls where the flow temperature of the boiler is automatically controlled based on an exterior temperature sensor.
Such controls are not expensive and can save 10-15% of energy.
As regards the TRV sensor - personally I would choose larger rad/lower flow temp over the minimal improvement in TRV sensor accuracy afforded by horizontal mounting, if there is a real problem with an overheating sensor, TRVs with remote capillary connected sensors are available.
Best of luck with your endeavors!