If the CPC CSA was designed on the assumption of a shock path impedance greater than 1kΩ, then there would be an appreciable risk that the shock current would be greater than 5mA in some people/situations - something you said they were attempting to avoid.
As bernard has said, shock path impedances vary considerably. The internal impedance of the body is very low (being essentially salt-ridden water), the great majority of the shock path impedance being in the skin at the two points of contact. That skin resistance varies according to the part of the body concerned (simplistically, how 'thick/horny' the skin is), the voltage and particularly the degree of 'wetness' of the skin (and 'wet because of sweating' is worse than 'wetted with pure water', because of the salt etc. content of the former) and all sorts of other factors - and is, as one might expect, roughly inversely proportional to the areas of contact. Since the 'internal body impedance' is low, the shock path current is much less dependent on path length than one might expect.,
You will find quite a range of figures around, one of the reasons being the difficulty in collecting data relating to the sort of voltages that interest us. One could safely and 'comfortably' measure body impedance in large numbers of situations in a large number of people if one used a very low voltage - but the results would not be very helpful in terms of, say, 230V. It's not uncommon to see average figures of 1kΩ - 2kΩ quoted for hand-to-hand impedance with dry skin (I think the IEC figures are about that), but that can fall to well below 1kΩ with wet skin, particularly if wet due to sweat. At the other extreme, with very dry skin in highly keratinised areas (like soles of feet), the impedance can be very high (50kΩ+).
Whatever, it will be interesting to know what figure your client provided, if you can find out (and even more interesting if you can discover where it came from). Looking at this the other way around, exactly how massive were these CPCs ("large earth cables") which were installed? Interesting, unless I've missed it, I don't think this is an approach to 'protection against electric shock' which the regs address, or even mention.
Kind Regards, John