Fair enough - but more than the 50V being mentioned and referred to as 'safe'.
Indeed - but, as I keep saying that 'unsafe' potential relative to truth earth is only actual 'unsafe' if either (a) one's equipotential zone is not as equipotential as it ought to be, or (b) if there is an adequate equipotential zone, but a person has part of their body inside (and able to touch an exposed-c-p), and part of their body outside, it.
Consequently, then, does it follow that you think it is a bad idea to TT outbuildings - and houses?
Not really - since, as you have just pointed out, even with TN the PD to true earth is more than high enough to be very dangerous IF either (a) or (b) above apply - so the fact that that PD is even greater with TT is really of no consequence (it was people other than me who raised that issue).
If (a) above applies, then there is not much to choose between TT and TN as far as safety/danger is involved - and, if one is concerned, one should make the zone more equipotential.
A judgement is necessary as to whether or not (b) applies and represents a degree of hazard that needs to be addressed. If one decides that it
does need to be addressed, the better (lesser of two evils, but far from foolproof) approach is probably to have TT with the rod very close to the door (as below). For what it's worth, in my house there are no exposed-c-ps touchable by someone standing outside the kitchen or cellar doors - so I'd be happy to have that situation with TN (if I had TN!). However, there
are such parts touchable from outside my greenhouse door - but that is TTd to a rod very close to the door.
Ok. but only in the (very) close vicinity of the rod. I presume the rod should be installed just outside the entrance of a shed - but is that how it is usually done?
As above, if (b) applies, then it is probably theoretically 'better' to have TT with the rod as close as possible to the door/window/whatever that could give access to an exposed-c-p within the house/building (as with my greenhouse).
Kind Regards, John