... and, strictly speaking, presumably changing to 4mm², if it is to continue to be protected by a 30A MCB.Yes ...But if that cable is too small it needs changing...
I disagree. It is a spur off a ring that just happens to connect to one end. A spur on a ring only need to be 2.5mm if it only feeds one double socket.... and, strictly speaking, presumably changing to 4mm², if it is to continue to be protected by a 30A MCB.
Kind Regards, John
Thanks. I was hoping that someone would say something like that, since it affords me an opportunity to canvas opinion about an issue which arose during a recent discussion I had.I disagree. It is a spur off a ring that just happens to connect to one end. A spur on a ring only need to be 2.5mm if it only feeds one double socket.
However, the question which arose during my discussion is the extent to which a designer can/should 'trust' people not to extend the circuit. In other words, how would people feel if I installed a "2.5mm² radial circuit" (not associated with any ring final), protected by a 32A (or even higher) MCB, which, currently, was feeding just one double socket?
It's not something that most people would even think about. The standard 'go to' method would be a standard arrangement of either a 16A or 20A MCB on a 2.5mm² T&E. After all it's what we install for circuits such as an immersion heater.how would people feel if I installed a "2.5mm² radial circuit" (not associated with any ring final), protected by a 32A (or even higher) MCB, which, currently, was feeding just one double socket?
Exactly. That was the point ... the only really issue is the OPD ....I think it is a trick question like your previous post. I would not, for a customer, put a 32A MCB on a 2.5mm² radial with a single double-socket so, I suppose, it would not arise without having to make other alterations.
Indeed, as you imply, that is a very tempting view. However, what was being suggested about a 32A 2.5mm² radial (electrically fine when it was installed, since it was supplying just one double socket) is that the unnecessarily high OPD rating almost impliedI am tempted to say that no consideration should be given to future incorrect extension - any more than considering people might surround the cable with thermal insulation ...
Exactly - but in those cases the OPD is appropriate to the cable.It's not something that most people would even think about. The standard 'go to' method would be a standard arrangement of either a 16A or 20A MCB on a 2.5mm² T&E. After all it's what we install for circuits such as an immersion heater.
That's exactly what was being said in the discussion I referred to - and, as you might imagine, some of the participants vociferously expressed the view that such a 'double standard' was irrational. One even asked if the C2 would go away if he connected both ends of a 6-inch length of cable to the MCB, in addition to the cable in question!!I know what you thinking about: if its OK for a 2.5mm spur from a ring-serving 32A MCB then it should also be OK if there wasn't a ring there. But I'd code it C2 if I found it while doing an EICR.