are there any issues that a socket outlet wired very close to the main dis board could casue to the RCD protecting it.
Had a mate call saying one socket on his downstairs ring main was tripping the RCD whenever something was plugged into it. He is new to the house and tells me the socket looks like a new one so could have been replaced and looks to be correctly wired.
In my humble opinion i reckon the socket outlet is more than likely the problem, but he made a statement that got me thinking, "is the socket too near to the RCD protection in terms of cable length.
My understanding of an RCD is that its an out of balance device that if the flux generated in the core doesnt blance out between the L and N, it induces the smaller coil and trips the breaker, so the length of cable between the RCD and the outlet is not a problem.
Am on on the right lines here, or does his statement hold any water so to speak ?