An RCD is not looking for circuit overload.
There must be earth leakage somewhere in the circuit. When the shower was replaced did the plumber check to make sure that the pipe fitting at the shower end is not leaking? i had a shower tripping an RCD once that was caused by water spraying up from an old compression fitting onto the live terminals.
with the fault occuring after a few minutes of use, it sounds to me like a water issue, which dries up by the time you begin to use the shower the next time.
its just strange that it occured with both old and new shower. Hence why i ask if the plumber checked the fitting, as most would just reuse the old.
Thanks for this. I think you may have cracked it. I bet the plumber didn't check that and probably just used the old fitting, assuming as we both did that it was the shower unit at fault.
Thank you. I appreciate your help on this.