As I've said, I think it pretty likely that an electrician would be able to confirm that your original plan (to replace the 32A MCB with a 40A one) would not only be OK, but would actually be the only correct and regulation-compliant thing to do - but you do really need that confirmation before you do it. It would be nice if you could let us know what the electrician says/does.
Good to see you after some time, but you do, yet again, seem to be singling me out for 'finding fault' with things I've written - on this occasion I don't think with much justification.
Uprating the MCB may fix the problem, but it's just as likely it won't be that simple. We don't know why the electrician selected the 32A MCB, but he may have installed 4mm cable. If this is the case, a 40A MCB will not be compliant (more importantly - not safe)
All true, but so what? - nothing I wrote was inconsistent with that. I previously suggested that its fairly unlikley that anyone would wire a shower circuit in 4mm² cable, but it's not impossible, which is why I only said that it is "pretty likely" that an electrician would be able to confirm that a 40A MCB would be appropriate (and
required for the shower) - but adding that it was necessary to obtain that confirmation before 'up-rating' the MCB.
I don't post very often because of threads like this. Rob has a real-life problem and was advised to get it checked. The early responders didn't suggest the cause or solution, as this needs investigation and cannot be resolved over the internet.
Quite so - which is why I said that an electrician needs to investigate and determine whether a 40A MCB should/could be fitted (and whether the cable is adequate for the shower). My only real contributions to this thread have been that indication that an electrician's investigation is needed and to respond to eric's suggestion that the OP should continue using a 32A MCB for a 9.5kW shower with:
That may well be true, but I'm not sure that we should be advising (or even suggesting) that anyone should deliberately overload an MCB (even if the cable is adequately protected) - not the least because it is non-compliant with regulations.
... and I'm a little surprised that even you should criticise me for any of that!
It then it turned into the equivalent of a C&G classroom question and Rob gets the 'preferred' answer and asked to let us know how he got on. Is that so we can see you are right again?
You really seem to 'have it in' for me
I've told the OP that an electrician needs to investigate and have told him what, IMO, is the 'likely' outcome of that investigation. Is it not reasonable that I should be interested in discovering whether or not I am correct in that opinion?
You tell us that you have this job writing major reports for medical companies. I assume this involves a lot of investigation and little/no guesswork, but your posts in this thread are guesses based on assumptions.
I've never 'told you' anything particularly specific about my professional life. It is certainly true that some aspects of my working life involve the writing of 'major reports' (or involvement in the writing thereof), for a spectrum of types of client. Some of that is purely mechanistic, but one of the important things a client often pays me for is my personal opinion (based on my knowledge, skill and experience) as to the 'likely' interpretation of the available information - you may call that "guesses and assumptions", but it's not how my clients see it!
Kind Regards, John