The only consistent and true advice in this thread is that an electrician (or anyone who knows what to do) should inspect the circuit.
Whilst it may have been non-compliant in the first place with a 32A MCB, 4mm² cable in method C would have been acceptable.
The current drawn is and has been the current drawn and the cable is still there.
The replacement with a 9.5kW shower should not have been done.
As it stands now, if inspected and found to be 6mm², method B or C, then the MCB rating can be increased.
Obviously 40A would be used - but subject to fault current being acceptable it does not matter if it were higher.
To be pedantic, 8.5kw @ 240V = 34A @ 230V and 32A x 1.13 = 36A.
Allowing for the time factor, the original installer may have considered this compliant and indeed used 4mm².
This would be far less onerous for the 32A MCB than a large cooker circuit which is perfectly compliant.
So, we don't know. Someone knowledgeable must inspect.
The only definite fault is the replacement with a larger a shower.
Whilst it may have been non-compliant in the first place with a 32A MCB, 4mm² cable in method C would have been acceptable.
The current drawn is and has been the current drawn and the cable is still there.
The replacement with a 9.5kW shower should not have been done.
As it stands now, if inspected and found to be 6mm², method B or C, then the MCB rating can be increased.
Obviously 40A would be used - but subject to fault current being acceptable it does not matter if it were higher.
To be pedantic, 8.5kw @ 240V = 34A @ 230V and 32A x 1.13 = 36A.
Allowing for the time factor, the original installer may have considered this compliant and indeed used 4mm².
This would be far less onerous for the 32A MCB than a large cooker circuit which is perfectly compliant.
So, we don't know. Someone knowledgeable must inspect.
The only definite fault is the replacement with a larger a shower.