2.5 is rated for a continuous current of around 27A..
cables can take a small orevload for a fair duration, but damage is being done..
your shower is pulling 30A ish, for a fairly short duration so it has time to cool down between uses..
if you put a larger shower on, say 8.5KW, then you're pulling 36A ish, so it's a bigger overload, and the cables will heat up faster and do much more damage to themselves and possibly the material they are run on / in / through, often to the point of causing fire in combustible materials such as floor joists...
As I've already said, it's time to call in a registered sparky and get a proper sized shower circuit installed and a new 10.5KW shower while you're at it..
cables can take a small orevload for a fair duration, but damage is being done..
your shower is pulling 30A ish, for a fairly short duration so it has time to cool down between uses..
if you put a larger shower on, say 8.5KW, then you're pulling 36A ish, so it's a bigger overload, and the cables will heat up faster and do much more damage to themselves and possibly the material they are run on / in / through, often to the point of causing fire in combustible materials such as floor joists...