Hi, A question for you experienced electricains out there.
My house is having a new consumer unit and I would like the ring main to stay wired as it is. A test was put on it and the results were as followed, r1 was 0.58, rn was 0.56 and r2 was 1.38, I think the cable is 2.5mm with a 1.0mm cpc. Is this ok? I am concerned about the resistance of r2 because the OSG stays r2 should be 1.67 times r1 or rn which is 0.96 which makes 1.38 quite high. Does this mean the ring main will have to be rewired in 2.5/1.5 T&E.
My house is having a new consumer unit and I would like the ring main to stay wired as it is. A test was put on it and the results were as followed, r1 was 0.58, rn was 0.56 and r2 was 1.38, I think the cable is 2.5mm with a 1.0mm cpc. Is this ok? I am concerned about the resistance of r2 because the OSG stays r2 should be 1.67 times r1 or rn which is 0.96 which makes 1.38 quite high. Does this mean the ring main will have to be rewired in 2.5/1.5 T&E.