Big_Spark
crafty1289 said:Use a 4-way consumer unit. Have the main incomer as a 30mA RCD.
Works for me.
Why four way...??
crafty1289 said:Use a 4-way consumer unit. Have the main incomer as a 30mA RCD.
Works for me.
crafty1289 said:Use a 4-way consumer unit. Have the main incomer as a 30mA RCD.
Works for me.
crafty1289 said:future expansion. got 2 blanks there at the moment. B32 ring (freezer, radio, lawnmower etc) and B6 lights. Budget didn't allow for customised outraegeous RCD arrangements
Big_Spark said:OK..well the shed should be fed with a 6mm² feed to ensure it can handle the potential load with everything you have said.
The Main Incomer should be a 100mA 40A Type S RCD.
I would suggest that each piece of equipment has it's own circuit and that the Pond pump, lawn mower socket and heater are fed on 30mA RCBO's. Whilst this is not a requirement it is advisable as you are having a freezer in there. It is s***s law that one would fail and trip the main RCD just after you leave for holiday!!
I suggest these as these are the most likely to cause nuisance tripping. DO NOT PUT THE FREEZER ON ANYTHING OTHER THAN AN MCB, they have a habit of tripping them, hence using the 100mA main RCD.
Big_Spark said:mdb, on the whole that is OK, but I would suggest that you use a RCD FCU for the outside lights and the socket that will feed the lawnmower certainly needs 30mA protection. You don't want to be tripping it and forgetting to reset it when you have a freezer on the same supply.
4mm² will proabably be electrically ok, but it may not comply with BS7671. Remeber, if you have the Tumble dryer running (12A) the freezer on (about 5A), the heater running (about 10A) and say the lawnmower going (say 10A) then you have a potential load of 37A, not including your lighting.
I understand that this situation may be rare, so is being shot, but the Police still wear bullet proof vests for a reason!!
I would use 6mm², the cost difference is small, and it will give greater protection if the supply does get loaded up. I would also suggest this be a 3 core SWA so the main earth is integral to the cable.
I assume that you made a typo with the RCD and that it is an 80A 30mA RCD, I don't recall ever coming across a 80mA RCD..
mdbalson said:Big_Spark said:Need some information.
TOTAL distance from House CCU to Shed CCU..
Total expected load in the shed...
What type of ingress protection does the shed have?
Total distance from House CCU to Shed CCU is about 5m or less.
Load in the Shed will be:
Freezer = 500w
Tumble Dyer = 3Kw
Heater 2Kw
Outside Floodlight =500w
Pond Pump =100w
Two sets of Low Voltage outside lights =200
Lawn mower =1Kw