Anyway, back to the question I asked again, I wasn't thinking about it at the time as I was too ****ed off, but basically doubling up a cable will only give you increased current carrying capacity as the current will be split. The volt drop will still be the same, they have decided they only want one shed wired now so circuit is reduced BUT, even so
25m (approx but better too long than too short!!) x2.5@20A = (18mVx20x25)/1000 = 9V
Approx 3m internal wiring x 2.5@20A = (18mVx20x3)/1000 = 1.08V
Approx 1m to light x 1.5@5A(FCU) = (29mVx5x1)/1000 = 0.145V
Total = 10.225V which is greater than 9.6V so no go.
With doubled up 2.5 you have two runs at 10A each, so 2x((18x10x25)/1000) = 9V, so no different.
Even if I used 4mm T+E internal you would have (11mVx20x3)/1000 = 0.66V, so new total would be 9.805V so still too high.
Even though it is borderline I'm still sticking to what I said, that they need 4mm SWA for the 25m run to the shed, doubling up 2.5mm SWA will make no difference.
I am right in what I'm saying aren't I? Wouldn't mind some clarifcation just to make sure I'm right!!
Unless I dropped the mcb at the house to 16A, this would bring the volt drop down on the cable run and so 2.5mm could be used, but would this be enough current for a single shed? 2 double sockets and a fluorescent, to supply a freezer and various tools? Dropping from 20A to 16A doesn;t seem a lot and would make the isntall doable with what they have, but wouldn;t exactly be future prrof. Not sure what to do