While I think daftpunk was being an asshole saying somethign was wrong without explaining why I do have some issues with this statement. it's mostly true but also quite misleading to the uninitiated.Rings and spurs are wired in 2.5mm cable. A ring has 2 paths back to the fuse or MCB whereas a spur only has one between itself and the ring so the total load is limited.
The requirement is for the cable to be able to safely carry 20A. What cable size is needed for this depends on cable tpe and installation conditions. 2.5mm is typical but it can be lower (MICC) or higher (thermal insulation, grouping factors etc)Rings and spurs are wired in 2.5mm cable.
The general principle is that overload protection must be provided unless overloads are considered unlikely.A ring has 2 paths back to the fuse or MCB whereas a spur only has one between itself and the ring so the total load is limited
The thing with an unfused spur is that there is no protection from overloads in the fixed wiring. So the regs only allow one single or double socket. Presumablly the assumption is that the two sides of a double socket are unlikely to be heavilly loaded at the same time.
Whereas with a fused spur or a radial circuit with the correct breaker there is overload protection in the fixed wiring, and therefore no need to set a limit on the number of scokets.
The regs are somewhat inconsistent though in that multiple sockets clustered at the end of the ting are very nearly as bad electrically as multiple sockets on a spur. Yet the latter is explicitly prohibited while the former is not.