I don't want to pick on you either; but you have claimed to know about rings and radials.
Yet you have said:
If you know about radials then you should know that a standard 4mm radial is protected by a 32A cpd. A 20A cpd would be required if the radial is in 2.5mm²
Yet you have said:
, I'm assuming it needs to be either made into a ring or rewired 4mm/20A. .
If you know about radials then you should know that a standard 4mm radial is protected by a 32A cpd. A 20A cpd would be required if the radial is in 2.5mm²