"Linked" MCBs is a totally different issue - and something I have never seen in a domestic CU, so really a red herring.Please state what regulation, can't think of one, as to danger with a single 32 amp MCB any large load near the origin of the ring can cause an overload, with two 16 amp MCB's linked neither leg can be over loaded so if anything safer.
I've mentioned that danger - which, in itself, is probably enough to make it non-compliant. However, as I also said, there is also the issue of disconnection times. A fault near one end of the ring would leave relatively little current flowing through one of the MCBs until the other one operated, which could almost double the time before both ends of the circuit were disconnected, and hence the fault cleared.As to if not linked, with a three phase supply motor could single phase, but in a single phase supply only danger is if some one does not test for dead.
As above, 'linked' RCDs are a red herring, at least in relation to domestic installations. Two 'ordinary', unlinked MCBs (one at each 'origin' at the CU) would be just as bad with a figure-of-8 than with a simple ring.As with fig 8 I think not following normal practice is wrong even if no rules broken, but as with fig of 8 can't see what rule is broken using two 16A linked MCB's.
Kind Regards, John