We don't know. All the overhead supplies round here are PME.
Interesting the first electrician didn't point anything out - have they visited the property?
[/assumption]As ypu supply is over head cables the supply company ( DNO ) cannot garantee that they can provide an earth to your property. Damage to the overhead cable could disconnect an Earth wire but leave the Live still connected. Very hazardous if the house relies on the Earth from the supply network. Most networks combine the Earth and the Neutral onto the same wire but the effect is the same if that wire snaps.
We don't know. All the overhead supplies round here are PME.
Interesting the first electrician didn't point anything out - have they visited the property?