Why is this such a surprise? There's no requirement to do a full EICR before doing a CU swap.
True, but I think some readers of this forum may get confused. You don't have to look far in the archives to see many instances in which posters have been 'warned off' electricians who quote for a CU change without a prior EICR (or PIR as it would have been in those days).
I would imagine that a high proportion of CU chages are undertaken on installations that are sufficiently old that a full EICR would be advisable, and if that were done imemdiately prior to the CU change, then I would have thought that (provided only the CU change was done) only live tests would then have to be repeated after the CU change. Is that correct?
Kind Regards, John.
The problem is, John, to do a full EICR first, you will be required to complete a 'schedule of inspections' and a 'schedule of test results.
This EICR is on the existing installation, which includes the existing CU, (and protective devices etc), it would take you most of the day on an average 3 bedroom semi, cost the customer an additional £100 to £200 and it wouldn't be worth the paper it's written on the day after, when you change the CU.
You would then have to complete an EIC for the CU swap - with accompanying 'Schedules' - granted, you will transfer some of the results, but what a waste of time.
If the customer wanted a full EICR, that's up to them - it's their money after all.
The ESC recommends a full PIR (EICR) before a CU change, but goes on to say that if the customer won't pay for this, then a risk assessment can be made and, if satisfactory, the CU swap can proceed.
I tend to check with the customer, (during quotation), if there are any known problems or if there have been any alterations.
I would also inform them that any remedial work, would be quoted for seperately, if required.
ESC
....the initial approach should be to
persuade the customer that remedial action
should be taken to correct or remove any
immediate danger, potential danger or
condition that would cause unwanted tripping
of an RCD.
If I get the job, I would then check supply parameters, confirm earthing system and Ze, confirm adequacy of main protective bonding and then inspect layout of circuits to familiarise myself with the installation, in particularly lighting, to explore the possibilty of borrowed neutrals.
I would have asked the customer to remove all plugs from socket outlets before I arrived and I would then proceed with an IR test of the whole installation as one.
This, in my opinion, should be sufficient to then proceed with the CU change.
The remainder of the tests would be done with the new CU in situ - during the 'Initial Verification' procedure of the CU.