Should Part P get scrapped?

Can you make a case for the council tax payer subsidising DIYers and tradesmen who choose not to register?
Quite. That's why, amidst all the reservations I voice about Part P, you'll never find me moaning about the fees, other than to say that they should not make a 'profit' for LABC. If we are to have Part P, then, as you imply, the cost of non-self-certified notified work must be bourne by those undertaking/commissioning the work, not by Council Tax payers in general. The fees obviously should reasonably reflect the true cost to LABC, without any 'profit'.

Kind Regards, John.
 
Sponsored Links
The fees obviously should reasonably reflect the true cost to LABC, without any 'profit'.
Which, IMO, they demonstrably don't.

When I put a thermal store in the flat, LABC weren't sure if it was notifiable but after discussion decided it was - and charged me their minimum fee for minor works of (IIRC) about £75. The fee for minor electrical works was about £150 or £225 - the difference being whether I can supply test results or not.

So, it's £75 for them to pop round, see I've done what I said I would, post me a bit of paper.
Or, it's £150 for them to pop round, see I've done what I said I would, post me a bit of paper if it's electrical.
And another £75 if they have to get someone to test it.

So why, if I can provide the right test results, does minor electrical work cost twice as much as non-electrical work ? And I've heard of some LABCs charging £400 :eek:


On loop impedance teser checking, I wasn't thinking of checking that other than perhaps checking the house supply and later seeing if I get a similar result. For what I'm likely to be doing, it's not going to be an issue if it's a long way out (which it's not likely to be). Eg, If I were to add a circuit to a CU (which I'd probably get someone in to do as being cheaper than LABC fees), all I'd be interested in is "is the prospective fault current less than the breaking capacity of the breaker". If my tester says something like 1600A, and the breaker is rated to break 6kA, then the tester would need to be out by a factor of more than 3 - and unless my home supply changed quite dramatically, it would show up on a quick verification check. For doing R1, RN, R2 and IR checks - as you've pointed out, a few quality resistors in a box will do.
Of course, if I did get someone in, then I'd be able to cross check against his test results ;)

But I realise you guys have slightly different (more demanding) requirements to me.
 
The fees obviously should reasonably reflect the true cost to LABC, without any 'profit'.
Which, IMO, they demonstrably don't.
In some cases that is probably true - which is wrong and IMO should be corrected; I'm not even sure that it's lawful for them to 'make a profit' from such fees. However, you may be underestimating the true costs to a large bureaucratic organisation. For example, rightly or wrongly, when properly calculated, the true cost of merely receiving and responding to a letter can easily be £20-£30, and the true calculated cost of 'getting someone to pop around' might well surprise (or shock) you!

On loop impedance teser checking, I wasn't thinking of checking that other than perhaps checking the house supply and later seeing if I get a similar result.
In that case, as BAS has said, you don't really need more than one resistor.

For what I'm likely to be doing, it's not going to be an issue if it's a long way out (which it's not likely to be). Eg, If I were to add a circuit to a CU (which I'd probably get someone in to do as being cheaper than LABC fees), all I'd be interested in is "is the prospective fault current less than the breaking capacity of the breaker".
In fact, if you have a TN supply, you don't really have to measure Ze or PFC - both EIC and EICR forms will accept values obtained by enquiry from DNO.

However, if (as you hypothesise) you were adding a circuit, then I don't think it's true that your only interest would (or should) be in "is the prospective fault current less than the breaking capacity of the breaker". You would also be interested in the Zs of the new circuit, and the various forms would require that to be recorded. For your own purposes, R1+R2 of the new circuit would be adequate, but I somewhat doubt (am I wrong?) that officialdom would accept a Zs figures derived by adding measured R1+R2 to a Ze obtained by enquiry. Apart from anything else, such a calculated Zs may well be appreciably higher (albeit that's 'conservative') than the figure you would get with a live test with parallel paths present - which is the way it's usually done.

But I realise you guys have slightly different (more demanding) requirements to me.
I wouldn't say that is true of me. I built what I did in the days when I only had one MFT which had been obtained cheaply and which had not be calibrated for a long time. I therefore wanted not only to be able to check for any calibration drift from the time at which I purchased it but also to give myself some reasurance that the readings being obtained were not only consistent but also at least roughly correct.

Kind Regards, John.
 
It has scared a lot off, people now say that they are not allowed to do anything so dont. (even though they can do some stuff). Some of us just ignore it anyway so still do.
The problem is that it has scared off a good few people that didn't really need scaring off (knowledgeable, competent and conscientious DIYers and non-certifying electricians who would probably always do work properly and safely) but has not scared off a lot of the people that probably did need scaring off (uninformed DIYers or cowboy electricians, who may well not have the knowledge, ability or inclination to work properly/safely - and who simply ignoire Part P {if they've heard of it!}).

Kind Regards, John.
 
Sponsored Links
I'm not even sure that it's lawful for them to 'make a profit' from such fees. However, you may be underestimating the true costs to a large bureaucratic organisation. For example, rightly or wrongly, when properly calculated, the true cost of merely receiving and responding to a letter can easily be £20-£30, and the true calculated cost of 'getting someone to pop around' might well surprise (or shock) you!
I have emboldened the part I wish to discuss.

I am always astounded by the charges of these organisations - BT.,BG.,LA. etc. although not by the reaction of a customer should I submit a bill at the same rate. (BT £116 call out and £99 ph.)

I realise they have large overheads but surely this should be proportionate to the number of customers and amount of work and so the rate per job should not be that much more than a small company?
After all (for LA) it would be extravagant to have the town hall as their premises if they only had the same number of customers as I do.

What am I missing apart from waste and nest feathering.
 
I am always astounded by the charges of these organisations - BT.,BG.,LA. etc. although not by the reaction of a customer should I submit a bill at the same rate. (BT £116 call out and £99 ph.) I realise they have large overheads but surely this should be proportionate to the number of customers and amount of work and so the rate per job should not be that much more than a small company? .... What am I missing apart from waste and nest feathering.
I am also astounded, but that's how it seems to be - and it applies to most 'small and medium sized' companies as well as the giant companies and organisations to which you refer. Some of it is obviously due to unnecessary waste/inefficiency, and in some cases to excessive profits, but even without those factors, the true costs work out as almost unbelievably (to you and I) high.

It's not as a linear situation as you suggest. When an organisation gets above a certain (pretty small) size, it seems that the overheads start increasing disproprionately (sometimes seemingly exponentially!) to the volume of work (number of jobs/employees/turnover/whatever). The overheads really take off the moment one gets into the position of having (needing?) multiple hierarchical tiers of admin and management. In contrast, very small companies/organisations often have flexibility and/or spare capacity, and not much in the way of fixed overheads, such that the marginal costs of undertaking a particular job can sometimes be almost zero. I think it's also true that many, if not most, very small companies tend to undercharge, often because they don't realise how much it actually 'costs them' to have a telephone conversation or reply to a letter etc. People knock lawyers because of their 'stopwatches' and 4-minute charging, but at least they have an understanding of what time/cost they are devoting to their clients.

If you look at medium sized service organisations, you will often find that the break-even point requires that the time of employees be charged out at 5 or more times what they get paid. So, if an employee is paid £25k p.a (about £12.50/h for 40h/week), one might well see their time being charged out at at least £62.50/h, often a fair bit more than that. For more details, or 'justification' you would need to talk to a proper businessperson - I think I might be saying that 'small is beautiful' :)

Kind Regards, John
 
Recently received a leaflet from BG. offering £800 off the price of a new boiler.

I thought that meant they would give me £200 for letting them fit it.

Apparently not. :)
 
However, it's so unlikley that you would get seemingly unchanging results despite meter drift that I agree that your method would be reasonable if all one wanted to do was to undertake serial checks on the same meter to monitor any changes in results.
Which is what the box is for.


What put me off that approach is that I wanted my box to also be able to to give a reasonable indication of whether an 'unknown meter' was giving accurate absolute results - and that requires a series of 'known loop impedances' to check the meter with; your method (even with multiple switchable resistances) would only confirm a linear relationship between reported and true loop impedances, without detecting any systematic difference.
So you have a calibrated meter which measures a loop impedance at your test socket of 1.2Ω and 2.2Ω when you switch in the extra resistance.

And your uncalibrated meter measures 1.18Ω and 2.16Ω respectively.

Does that not tell you what you need to know?


You might just as well look for serial changes in the RCD tester's results with one of the RCDs in your home
Except this way the RCD is there, and handy to test at the same time without disrupting the house.
 
What put me off that approach is that I wanted my box to also be able to to give a reasonable indication of whether an 'unknown meter' was giving accurate absolute results - and that requires a series of 'known loop impedances' to check the meter with; your method (even with multiple switchable resistances) would only confirm a linear relationship between reported and true loop impedances, without detecting any systematic difference.
So you have a calibrated meter which measures a loop impedance at your test socket of 1.2Ω and 2.2Ω when you switch in the extra resistance.
And your uncalibrated meter measures 1.18Ω and 2.16Ω respectively.
Does that not tell you what you need to know?
As I said (per what you've quoted), one needs a 'known loop impedance' in order to evaluate an unknown uncalibrated meter. If one also has a calibrated meter, then one effectively has a known loop impedance to use for the test. Indeed, even without your switched resistance, if the calibrated meter read 1.2Ω and the uncalibrated one 1.18Ω when measuring the same loop impedance, then I would be pretty happy with the uncalibrated meter - although I agree that the results obtained by switching in a resistance would give further reassurance. However, the basis of your test would be comparison of the calibrated and uncalibrated meter - the switchable resistance being a little bit of icing on that cake.

However, as I wrote this morning, I built the box at a time when I did not have a calibrated meter. All I had was the uncalibrated one, so I would have had no idea as to whether the 1.18Ω and 2.16Ω readings were anywhere near the truth. That's why I had to create an articifical 'known loop impedance'. Admittedly, there was a bit of a Catch 22, in as much as I had to borrow a calibrated meter in order to confirm that I had indeed created the 'known loop impedance' I thought I'd created - but I only had to do that once!

You might just as well look for serial changes in the RCD tester's results with one of the RCDs in your home
Except this way the RCD is there, and handy to test at the same time without disrupting the house.
That's true, but I still don't think that relying on the 'expected' behaviour of an RCD (whether an in-service one or one in your box) is a very satisfactory way of evaluating an RCD tester. As we know (one of the reasons for testers!) the fact that it hasn't operated very often is the last of reasons for assuming that its behaviour will be unchanged from year to year!

Kind Regards, John.
 
Is there a circut diagram available for this box anywhere?
 
In some cases that is probably true - which is wrong and IMO should be corrected; I'm not even sure that it's lawful for them to 'make a profit' from such fees. However, you may be underestimating the true costs to a large bureaucratic organisation.
I think you misunderstood my point. Whether the actual value is justified or not is another matter, but if I do minor electrical DIY work and present test results then I'll be charged £150 for them to pop round, look at what I've done, and then post a certificate. If it's minor non-electrical work then they can do the same amount of work for £75 - so why the difference ? If I can't supply test figures then they charge an additional £75 which will be to cover the cost of testing my work - which seems "proportional" given the cost of (for example) getting a PIR done.
 
I think you misunderstood my point. Whether the actual value is justified or not is another matter, but if I do minor electrical DIY work and present test results then I'll be charged £150 for them to pop round, look at what I've done, and then post a certificate. If it's minor non-electrical work then they can do the same amount of work for £75 - so why the difference ?
I don't think I misunderstood your point; my reply was about the general principles. Needless to say, I can't explain, let alone justify, the differences you highlight, but there may possibly be a rational explanation (e.g. maybe they know from their experience that, on average, 'popping round' in relation to electrical work involves more time than for non-electrical work) - you'd have to ask them. I have to say that, in terms of how these things usually work out, for a large organiation to do any 'popping out' (including travel and travel time) for £75 seems pretty 'cheap'.

If I can't supply test figures then they charge an additional £75 which will be to cover the cost of testing my work - which seems "proportional" given the cost of (for example) getting a PIR done.
That certainly doesn't sound unreasonable to me.

Kind Regards, John.
 
In some cases that is probably true - which is wrong and IMO should be corrected; I'm not even sure that it's lawful for them to 'make a profit' from such fees. However, you may be underestimating the true costs to a large bureaucratic organisation.
I think you misunderstood my point. Whether the actual value is justified or not is another matter, but if I do minor electrical DIY work and present test results then I'll be charged £150 for them to pop round, look at what I've done, and then post a certificate. If it's minor non-electrical work then they can do the same amount of work for £75 - so why the difference ? If I can't supply test figures then they charge an additional £75 which will be to cover the cost of testing my work - which seems "proportional" given the cost of (for example) getting a PIR done.

Ive recently been informed by my LABC that they will only accept testing figures from a registered spark. .
However this makes me question the legality of such a position, a competent person can carry out a PIR/EICR registered or not so surely the LABC stating they will only accept a set of test results from a registered spark must fall foul of some restrictive trade/monopoly rules.
 
Ive recently been informed by my LABC that they will only accept testing figures from a registered spark.
If it is important to you ask them to explain how they can be certain that the registered spark has actually carried out testing or has just filled in the expected values without putting a meter to the installation.

If a DIYer provides a set of values and a documented report of how the testing was done, maybe including photographs, them the LABC is out of order to refuse to accept them.
 
  • Thanks
Reactions: STI
Ive recently been informed by my LABC that they will only accept testing figures from a registered spark. .
However this makes me question the legality of such a position, a competent person can carry out a PIR/EICR registered or not so surely the LABC stating they will only accept a set of test results from a registered spark must fall foul of some restrictive trade/monopoly rules.
That doesn't surprise me. I know nothing of the legality, but suspect that an LABC is free to work to whatever 'rules' it feels necessary in order to satisfy themselves that Part P has been complied with. One has to have some sympathy, since it would be naieve of them to blindly accept pieces of paper on which words and numbers had been written by some 'Tom, Dick or Harry' about whom they knew nothing - so I don't know what the answer is for them.

A PIR/EICR is a rather different matter. It is merely a bit of work commissioned by the owner of an electrical installation and, as far as I am aware, is not subject to any controls. Whether or not the resulting certificate would be taken seriously by any third party obviously depends upon who has provided the report.

Kind Regards, John.
 