If, from your main earth terminal (usually in the CU) to structural metalwork (pipework) has a resistance of greater than 22ohms then 'earthing' is not required.
If, from your main earth terminal (usually in the CU) to structural metalwork (pipework) has a resistance of greater than 22ohms then 'earthing' is not required.
If, from your main earth terminal (usually in the CU) to structural metalwork (pipework) has a resistance of greater than 22ohms then 'earthing' is not required.
yup that busy finding the ohm symbol, which I didn't I forgot the (capital) K as in 22KΩ
Using an MFT:
I = V / R;
I = 500V / 22000Ω = 0.023Amp
If the fault was on a single phase 230V supply the current that would flow between the conductive parts would be only 0.0115Amp or 11.5 mA. Just above the 'let go' of 10mA.
It's the other way round.
10mA is used to determine the resistance.
230V / 10mA = 23,000Ω
Never see the point of deducting 1,000Ω for the human body.
It's not going to be 21,999 or 23,001 is it?
More likely to be 240V anyway, so 24,000Ω
It's the other way round.
10mA is used to determine the resistance.
230V / 10mA = 23,000Ω
Never see the point of deducting 1,000Ω for the human body.
It's not going to be 21,999 or 23,001 is it?
More likely to be 240V anyway, so 24,000Ω