At the beginning of the year we had our bathroom completely refitted and along with that installed a new Mira Sport Max air boost shower. As it is 10.8kW rated, we needed to upgrade all the cabling etc and that was done.
Everything has been mostly fine, but it has recently started tripping out on the consumer unit. At first this was just when the washing machine was on, or if the unit was on for longer than 30 minutes (EDIT: or so it seems, I guess this is when I've shaved in the shower and taken longer than usual. My wife is probably downstairs using the kettle, TV turned on, computers plugged in etc - perhaps increasing the load on the system?). For the first time today, it tripped it without anything else on, bar normal appliances on standby etc - twice. Once within about 15 minutes of the shower being on, and then 5 minutes or less after being reset.
I've had a look at our consumer unit and noticed a couple of things:
1) I'm sure in the manual, it says there should be a 45A as the recommended MCB size. If I've understood that correctly, I can see that the label on ours says 40A - see picture below. I cannot pull it out to check what is actually fitted as you can see in the picture it seems to be wedged in... (labelled below it as Shower)
View media item 60401
2) I also noticed that there is a warning on the consumer unit that says the total load should not exceed 100A "For all circuits total load not to exceed 100 A" (see picture above at bottom right corner). From totalling everything on the top of the fuses, I can see that the total across all of them does exceed this (see pics below). Sockets 30A, Sockets 30 A, Shower 40A (should be 45A), Water Heater (20A), Lights 5A, Lights 5A.
View media item 60402View media item 60403View media item 60404
Is this likely to be a simple case of upgrading the consumer unit to one that can cope with the load?
Everything has been mostly fine, but it has recently started tripping out on the consumer unit. At first this was just when the washing machine was on, or if the unit was on for longer than 30 minutes (EDIT: or so it seems, I guess this is when I've shaved in the shower and taken longer than usual. My wife is probably downstairs using the kettle, TV turned on, computers plugged in etc - perhaps increasing the load on the system?). For the first time today, it tripped it without anything else on, bar normal appliances on standby etc - twice. Once within about 15 minutes of the shower being on, and then 5 minutes or less after being reset.
I've had a look at our consumer unit and noticed a couple of things:
1) I'm sure in the manual, it says there should be a 45A as the recommended MCB size. If I've understood that correctly, I can see that the label on ours says 40A - see picture below. I cannot pull it out to check what is actually fitted as you can see in the picture it seems to be wedged in... (labelled below it as Shower)
View media item 60401
2) I also noticed that there is a warning on the consumer unit that says the total load should not exceed 100A "For all circuits total load not to exceed 100 A" (see picture above at bottom right corner). From totalling everything on the top of the fuses, I can see that the total across all of them does exceed this (see pics below). Sockets 30A, Sockets 30 A, Shower 40A (should be 45A), Water Heater (20A), Lights 5A, Lights 5A.
View media item 60402View media item 60403View media item 60404
Is this likely to be a simple case of upgrading the consumer unit to one that can cope with the load?