You can still purchase the Proteus 640/2 40A Type 2 M4 from new and there was also a 45A version.
I may have misunderstood, there was a mention of things tripping out around the house.It's not the RCD which is tripping.
It's a 40A MCB supplying a 45A load.
Can I please have this confirmed, is it the 40A device only that trips causing power-loss to shower or is it the RCD that trips causing power-loss to shower, sockets and heater?
I found this http://www.proteusswitchgear.co.uk/product_details.asp?product=1330 which states it is obsolete so likely they had to buy old or second hand so not their fault they have clearly tried to keep down costs for you.
If that is the case then the rating needs the be suitable for the load, but the cable size has to also be suitable for the fuse rating. That is why it is important to know cable sizing and the route and method that the cable is installed.It is just the 40A device tripping out causing power loss to the shower.
If that is the case then the rating needs the be suitable for the load, but the cable size has to also be suitable for the fuse rating. That is why it is important to know cable sizing and the route and method that the cable is installed.It is just the 40A device tripping out causing power loss to the shower.
Is the installer still contactable, you should have had certificates and a building control notification, as a new circuit was installed for the upgrade.
When you don't get certificates, generally something stinks!
Please read edit!
The manufacturers instruction quiet clearly state a 45A device should be used, as trained engineers we are instructed to follow the manufacturers instructions and the 40A device should not have been used.
Although it maybe the case that some appliances can run for a period of time, without an overload being induced, it is bad practise to under rate a circuit.
A 10.8KW shower pulls 45amps at 240volts
A 40 amp MCB will allow 45amps to pass for quite a while before it trips. Sorry I don't have type 2 graphs to hand.
Looks like a 45A breaker is required, but before changing, it will need someone to positively check that
1. the cable that you have there is capable of carrying 45amps
2. the EFLI is within limits
3. that there are no other faults on the circuit
Why did they shoehorn a Protek breaker in a Wylex board
Assuming it is that simple, and all we need to do is change the 40A device to a 45A one, can you explain to me in plain English what is happening to the shower? I don't understand why it would run at all, or why it decides to randomly fail, or what causes it to fail. I appreciate that this is probably pretty basic stuff, but I just want to understand (on the basis of that assumption) a) what is happening, and b) why, in real English, not engineers speak!