Shower trips the fuse on the consumer unit

Sponsored Links
That 40A MCB is NOT new. Not sure of date but it was around 1990 when we changed from 1, 2, 3, and 4 to B, C, and D MCB ratting may have been earlier. So swapping the 40A type 2 for a 40A type B will likely cure the problem.

Also the MCB does not seem to be fitted square and I have in the past had problems where the plastic of the MCB is warped by strain on cables and it trips at the wrong current.

I am not up to date maybe one of the others can say if MCB's are still made for that board. It may be it's an obsolete board and the installer has had to buy old stock from some where to fit the board.

That type of Wylex MCB isnt available anymore, The nearest match that wholesalers supply around here (Manchester) is Proteus , I`d guess the Board is at least 20 yrs + old , If I`d have done the job , I would have preferred to use a standalone Consumer Unit , to supply the Shower.

Lucky
 
Interestingly it was the plumbers who suggested this may need to be done, not the electrician (they said that before they contacted him, just to warn us about the cost implication).

I think that's what I'm going to discuss with the electrician when he comes round.
 
Sponsored Links
I guess in that case, I'm going to be asking for the best option, be that entirely new units to replace existing or whatever then. Stupidly overpaid to nearly pay off a new sofa the other day...oh well, bring on payday!
 
Just googled the 40A thing on the 10.8kW Mira Sport max and it seems to be discussed in various places, including on this forum previously with many recommendations stating "40A will be fine".
It's certainly anything but 'fine', but nor should it really be a reason for MCB tripping ....

...a B40 MCB should be able to carry 45A (10.8kW at 240V) indefinitely without tripping. Even if the shower managed 10.8kW at 230V (i.e. ~47A), which I very much doubt it would, it should still take a very long time (well over 2 hours) to trip a B40.

...but it certainly is not an aceptable, or reg-compliant, practice to have an MCB rated for less than the circuit's load current - so definitely not 'fine'!

Kind Regards, John
 
I always install a 50A supply for 10.8kW showers. It saves all this hassle, and 50A breakers are readily available straight off the shelf at the wholesalers.

If the existing CU won't take a 50A breaker, then it's up to the customer as to wether they want the whole CU replaced, or the tails splitting and a stand alone unit fitting.

Bodging jobs always comes back to bite you sooner or later.
 
Just googled the 40A thing on the 10.8kW Mira Sport max and it seems to be discussed in various places, including on this forum previously with many recommendations stating "40A will be fine".
It's certainly anything but 'fine', but nor should it really be a reason for MCB tripping ....

...a B40 MCB should be able to carry 45A (10.8kW at 240V) indefinitely without tripping. Even if the shower managed 10.8kW at 230V (i.e. ~47A), which I very much doubt it would, it should still take a very long time (well over 2 hours) to trip a B40.

...but it certainly is not an aceptable, or reg-compliant, practice to have an MCB rated for less than the circuit's load current - so definitely not 'fine'!

Kind Regards, John

What would happen if there was a voltage drop?

Say 220volts, that's 49 amps..how long would a 40a mcb pass 49amps?

Just a thought...
 
Just googled the 40A thing on the 10.8kW Mira Sport max and it seems to be discussed in various places, including on this forum previously with many recommendations stating "40A will be fine".
It's certainly anything but 'fine', but nor should it really be a reason for MCB tripping ....

...a B40 MCB should be able to carry 45A (10.8kW at 240V) indefinitely without tripping. Even if the shower managed 10.8kW at 230V (i.e. ~47A), which I very much doubt it would, it should still take a very long time (well over 2 hours) to trip a B40.

...but it certainly is not an aceptable, or reg-compliant, practice to have an MCB rated for less than the circuit's load current - so definitely not 'fine'!

Kind Regards, John

What would happen if there was a voltage drop?

Say 220volts, that's 49 amps..how long would a 40a mcb pass 49amps?

Just a thought...

For me as the uninitiated, can you explain to me what that would do/how long it would take, and what might cause that?
 
Also I've checked the cabling coming out of the consumer unit and it says something which I presume means made in Doncaster, and 10.0 which I assume relates to the cable size.
 
What would happen if there was a voltage drop? Say 220volts, that's 49 amps..how long would a 40a mcb pass 49amps? Just a thought...
It doesn't work like that - this is simple GCSE physics. A shower is a dumb (passive) heating element that can't compensate for a lower voltage by increasing the current so as to achieve the power stated on the box (i.e. 10.8kW) - so, if the voltage falls (to 220V or whatever, the current would also fall, not rise.

The 10.8kW rating very probably relates to the power that would be achieved at 240V (they do that to make their showers sound more powerful). That would be 45A. If that were the case, then as the voltage fell below 240V, so would the current fall below 45A.

Kind Regards, John
 
What would happen if there was a voltage drop?
Say 220volts, that's 49 amps..how long would a 40a mcb pass 49amps
It doesn't work like that.
Current and Wattage(Power) increase and decrease with voltage on resistive loads because the resistance (impedance) is the only constant.

10800W @ 240V = 5.33Ω (P = V x R)

The current would rise if the voltage rose to 245 or 250 (46.9A @ 250V).
 