Do the regulations say anything about connecting the MET of a PME system to an earth rod ?
I can recall being told that connecting the neutral derived "earth" of a PME supply to an earth rod was not permitted.
So what is this lead pipe other than a very effective earth rod that also delivers water. ?
Depends on whether
[1] the other end of the lead pipe connects to a metal water main that is bonded to the sub-stations neutral and hence not an earth rod.
[2] the other end of the lead pipe connects to a plastic metal water main and hence an earth rod
[3] the lead pipe connect to any other metallic pipes that feed other houses and are in metal to metal contact with the bonded pipe work in those houses.
My opinion is to treat it as a plastic pipe and bond only to the copper pipe work if it is a PME supply or if it is a TT supply then consider using the lead water pipe as a SUPPLEMENTARY earth "rod", supplementary to the main earth rod.
I can recall being told that connecting the neutral derived "earth" of a PME supply to an earth rod was not permitted.
So what is this lead pipe other than a very effective earth rod that also delivers water. ?
Depends on whether
[1] the other end of the lead pipe connects to a metal water main that is bonded to the sub-stations neutral and hence not an earth rod.
[2] the other end of the lead pipe connects to a plastic metal water main and hence an earth rod
[3] the lead pipe connect to any other metallic pipes that feed other houses and are in metal to metal contact with the bonded pipe work in those houses.
My opinion is to treat it as a plastic pipe and bond only to the copper pipe work if it is a PME supply or if it is a TT supply then consider using the lead water pipe as a SUPPLEMENTARY earth "rod", supplementary to the main earth rod.