Easy mistake to make. As I have said we also made the mistake. On a narrow boat we had a 4 amp supply and we though use that to charger batteries then have an inverter to give us the 3kW (6kW peak) we wanted.
However theroy was great practice was not. The inverter has an array of around 30 FET's each with a blade type 16 amp fuse and it hopes the resistance through the fuse is enough to ensure power sharing and up to about 1.5kW it did but at 2.8kW the kettle it just didn't work.
With a 24 volt or 48 volt system likely it would have worked but 12 volt is just too low and at 250 amp cables are also a problem. We used 360 Ah of battery which really was not enough and a 25 amp step charger.
The grandchildren meant that the boat was sold so the problem went away for us, the new owner swapped to a true sin wave inverter no where near as big.
Having learnt the hard way I hope I can stop others from making the same mistake.
However theroy was great practice was not. The inverter has an array of around 30 FET's each with a blade type 16 amp fuse and it hopes the resistance through the fuse is enough to ensure power sharing and up to about 1.5kW it did but at 2.8kW the kettle it just didn't work.
With a 24 volt or 48 volt system likely it would have worked but 12 volt is just too low and at 250 amp cables are also a problem. We used 360 Ah of battery which really was not enough and a 25 amp step charger.
The grandchildren meant that the boat was sold so the problem went away for us, the new owner swapped to a true sin wave inverter no where near as big.
Having learnt the hard way I hope I can stop others from making the same mistake.