What a lot of questions
The fuseboard is metal clad, and all the line and neutral conductors for each circuit are run in the same tube, so no problem there.
The socket circuits apper to be wired in 7/.029, so should be OK.
The tube coming into the left of the board is PVC conduit supplying a ring final circuit on a 16A RCBO. It is fairly new, and that is where the CPCs go.
Now here is the real problem.
Many of the sockets supplied from this board look like this:
They are relying on the old steel conduit as the CPC.
Not the best photo, but behind this DB is the original flush mounted fusebox where the conduits terminate.
Now, which ever numpty did this board change didn't bother to take a link from the earth bar in the new DB to the conduits in the old DB.
The readings for R1+R2 at all the circuits averaged between 2.5Ω to 4Ω.
Also, circuit one supplies a socket on a 6A MCB. The cleaner was complaining to us that her vacuum keeps tripping this socket
The RCBOs are connected up properly for polarity.
Oh and one of the conduits leaving the top left of the board, the lock nut wasn't on even finger tight