You don't have to 'do' anything special. When you measure the Zs from any point in a ciruit (like at it's end), you are, by definition, measuring the impedance of the entire loop (through which fault current flows), all the way back to the substation.Hi John, Ah sorry, I didn't realise the impedance was measured out to the substation. How on earth do you measure that?!
That may work, but I wouldn't personally put too much money on that never tripping at compressor start-up. Whatever the compressor's documentation may say about the inrush current, it could probably be anything up to about 10 times the running current - a C32 would be more likely to tolerate that than a B40I think I will just put another B40 in the garage to protect this new circuit,
Well, as before, you can't even be certain, without measuring it, that the Zs would be low enough for a B40, let alone a C32.I think previously I thought 6mm cable was only rated for 30-something amps, just realised that clipped direct it's 46a so a B40 would do the job fine and I don't need to worry about Zs etc?
Yep. The same would be true if you had a C32 in the garage. If you had tripping problems, the solution would, I suppose, be to have a C40 in the house (Zs permitting).I guess the use of the B40 on the new circuit would mean that the B40 upstream in the house could trip first in the event of an overload but I suppose that's fine?
Kind Regards, John