With MCBs that's definitely the difference between 1P+N and DP.
Thanks - so as I believed. I think this discussion may be getting a bit confused by the muddling up of DP sensing and DP switching.
I think the requirement for overcurrent protection of both live conductors is a matter of fault protection (i.e. L-E faults) rather than overload/short protection. Back when municipial metal water supply pipes were used as huge earth electrodes it was possible to have TT supplies without RCDs or ELCBs and I suspect the requirement for DP protection dates back to these times.
I don't really understand how that ever can ever have been used as an argument for having over-current
sensing in the neutral, since none of the fault current flows through the neutral in the case of an L-E fault such as you mention.
As for achieving adequate OPD-based fault protection (i.e. no residual current devices) in a domestic installation, I suppose that, as you say, it might have just about been possible when TT earths consisted of networks of underground water pipes, but I don't think it is realistic when reliant on domestic TT electrodes (with no/little bonded underground metal pipes), since most domestic TT electrodes would not have a low enough impedance for it even to work with a 5A / 6A circuit, let alone anything larger!
However, as above, even 'back then' I don't see how it would have been an argument for neutral current sensing.
Fusing of the neutral has indeed very much been allowed but many countries in the world, including the UK, banned single-pole overcurrent protection of neutrals around a century ago. Double-pole MCBs on the other hand are still perfectly acceptable as they break both conductors of a single-phase circuit at the same time and that's the important difference..
Sure, there's no problem with any devices which have DP
switching, since both poles inevitably get disconnected together. The potenbtial problem is obviously with DP
fusing - since there is then the possibility that, in the case of an excessive current (through both L and N) due to overload or an L-N fault might result in just the neutral fuse blowing, leaving the L fuse intact.
Many countries consider the neutral of a TT supply to be earthed well enough not to require fault protection (because it can't assume a significant voltage to earth) but as far as I know some, e.g. Spain, do not and require fault protection, and double-pole MCBs are one way of achieving that, if a dubious one assuming your earth impedance isn't particularly low.
Again, we're not really talking about whether or not the neutral "needs fault protection" but, rather, whether
over-current sensing in the neutral is needed. As I've said, other than in the presence of pretty bizarre wring error or faults, there is never going to be excessive current in the neutral but not in the corresponding line, is there?
Kind Regards, John