Scottish building regs (domestic technical handbook) 2010. Text hasn't changed since last version 2005:
"Outlets and controls of electrical fixtures and systems should be positioned at
least 350 mm from any internal corner, projecting wall or similar obstruction
and, unless the need for a higher location can be demonstrated, not more
than 1.2 m above floor level. This would include fixtures such as sockets,
switches, fire alarm call points and timer controls or programmers. Within
this height range:
• light switches should be positioned at a height of between 900 mm and
1.1 m above floor level;
• standard switched or unswitched socket outlets and outlets for other
services such as telephone or television should be positioned at least
400 mm above floor level. Above an obstruction, such as a worktop,
fixtures should be at least 150 mm above the projecting surface.
Where socket outlets are concealed, such as to the rear of white goods in a
kitchen, separate switching should be provided in an accessible position, to
allow appliances to be isolated."