Not is if is set to 500V, However I would still recommend disconnecting it as it could give false readings..depending on the test you are doing of course
Tried a little test - cabled up an FCU with a neon indicator. Does indeed give false readings on a L-N test - 265k.ohms, vs >1.999G with the FCU switched off. Actually, I think a better term would be "misleading"
Neon undamaged by the test (500V - zapped it several times), which should come as no surprise to anyone who thinks about the peak voltage the neon normally sees 100 times a second. Doh
Maybe I'll try 1kV in the interests of science
Have now done the 1kV test - same results, & neon lived to tell the tale...
Ban, the problem with this method of testing is that it is actually incorrect anyway.
When doing an insulation resistance test on a circuit, you should disconnect spurs and test the legs individually, so the neon should never be an issue anyway.