ban-all-sheds said:
Will an insulation test damage the neon indicator in an FCU?

Not is if is set to 500V, However I would still recommend disconnecting it as it could give false readings..depending on the test you are doing of course :)
 
The only snag is that you can't disconnect the neon in an FCU (well, not in the ones I've got).

I could switch them off, but then the insulation test wouldn't extend to the circuits served by the FCUs...
 
Tried a little test - cabled up an FCU with a neon indicator. Does indeed give false readings on a L-N test - 265k.ohms, vs >1.999G with the FCU switched off. Actually, I think a better term would be "misleading"

Neon undamaged by the test (500V - zapped it several times), which should come as no surprise to anyone who thinks about the peak voltage the neon normally sees 100 times a second. Doh :oops:

Maybe I'll try 1kV in the interests of science :eek: :evil:


Have now done the 1kV test - same results, & neon lived to tell the tale...
 
Sponsored Links
Ban, the problem with this method of testing is that it is actually incorrect anyway.

When doing an insulation resistance test on a circuit, you should disconnect spurs and test the legs individually, so the neon should never be an issue anyway.

What occurs in practise is another matter :)
 
mmmm.

And also lets not forget the possibility of surge protected sockets in the circuit...
 