Just to clarify for the hard of thinking reading this thread, what Danny stated regarding the 'Y' plan, this refers to a mid-poss valve; this valve will never not have an open port, even when all thermostats are satisfied, the hot water port will remain open, so this will even accommodate pump over-run. Therefore no by-pass valve is required.
[
Just to clarify for the hard of thinking reading this thread, what Danny stated regarding the 'Y' plan, this refers to a mid-poss valve; this valve will never not have an open port, even when all thermostats are satisfied, the hot water port will remain open, so this will even accommodate pump over-run. Therefore no by-pass valve is required.
And if an unvented cylinder is fitted on a y-plan and its overheat stat has tripped????
just food for thought /discussion
Matt
And if an unvented cylinder is fitted on a y-plan and its overheat stat has tripped????
just food for thought /discussion
Matt
This is why an unvented cylinder must have a spring-closed zone valve fitted and wired up to the overheat stat. Even if it is a Y-plan/Mid-position
Just to clarify for the hard of thinking reading this thread, what Danny stated regarding the 'Y' plan, this refers to a mid-poss valve; this valve will never not have an open port,
where do u live
In Wigan. Ashton in Makerfield to be a wee bit more specific.
But that statement is a fact my little Engerland Geordie chum, a 'Y' plan never has both outlet ports closed, if anyone is daft enough to fit two valves to control the HW cylinder, well, they need medication.......................An unvented cylinder should always be on an 'S' plan.
Under whar circumstances? When? Not haveing a dig at you, mearly looking for furher education/ information.a mid position valve always has a port open, true but what I'm saying is there are y-plan systems that can have all flow blocked off(unless you have an adequate bypass)
matt1e wroteUnder whar circumstances? When? Not haveing a dig at you, mearly looking for furher education/ information.a mid position valve always has a port open, true but what I'm saying is there are y-plan systems that can have all flow blocked off(unless you have an adequate bypass)
no mate, control wise its a y-plan(the safety valve will normally be held permenantly open on time control whilst the cyl stat will control the 3-port as normal) maybe it should be given another clasification y/s-plan perhaps!Matt, Y plan and UV cylinders is an anomaly which for all intent and purposes is really an S plan.
no,around the 5th page discussion moved on to Y plan as in cylinder and TRVed CH zones, needing a bypass- niether vented or unvented were mentioned,hence my first postDiscussion if I can remember correctly 9 pages on, is to do with Y plan as in vented cylinder and TRVed CH zones, needing a bypass.
as I mentioned earlier I was being pedantic and wanted to give a littleAnd if an unvented cylinder is fitted on a y-plan and its overheat stat has tripped????
just food for thought /discussion
Worcester Ri Mi's do state that 'generally a bypass is not nesessary on a Y plan system as one of the ports is open to flow'.
Just some common sense required I think. Chris