You wait for a supply cable problem for 6 months and then all of a sudden you get three turning up on the same day. Sorry, no pictures this time...
The one I went to had a Zs of 140 on TN-S. When I got there, there was a PME-style cutout with nothing attached to the earth terminal.
But, hanging out of the bottom of the cutout was a bit of solid strand bare copper earth wire.
Rang the DNO Manweb. She said there is no earth terminal & we want £100 to supply one. I said there was a pre-existing earth terminal that had never been connected to and she had better send someone out because the high Ze was dangerous. A guy turned up prompt as anything & connected the solid strand into the cutout earth terminal. Think it should have been a bit thicker, meself!! He said if you want 16mm², you have to pay for it.
Anyhow, we got 0.3 with it, but how much fault current would it carry before frazzling?
The next one was no earth on a supply I have to go and eyeball next week.
The last one was good: Got a call from a colleague saying he couldn't get a Ze off the tails. He got a voltage of 154V, and on pressing the Alphatek start key, he got PE, indicating no earth.
But, on a ZS, he got 245V.
I presumed the neutral was breaking down. Call the DNO quick!!
You wait for a supply cable problem for 6 months and then all of a sudden you get three turning up on the same day. Sorry, no pictures this time...
The one I went to had a Zs of 140 on TN-S. When I got there, there was a PME-style cutout with nothing attached to the earth terminal.
But, hanging out of the bottom of the cutout was a bit of solid strand bare copper earth wire.
Rang the DNO Manweb. She said there is no earth terminal & we want £100 to supply one. I said there was a pre-existing earth terminal that had never been connected to and she had better send someone out because the high Ze was dangerous. A guy turned up prompt as anything & connected the solid strand into the cutout earth terminal. Think it should have been a bit thicker, meself!! He said if you want 16mm², you have to pay for it.
Anyhow, we got 0.3 with it, but how much fault current would it carry before frazzling?
The next one was no earth on a supply I have to go and eyeball next week.
The last one was good: Got a call from a colleague saying he couldn't get a Ze off the tails. He got a voltage of 154V, and on pressing the Alphatek start key, he got PE, indicating no earth.
But, on a ZS, he got 245V.
I presumed the neutral was breaking down. Call the DNO quick!!