Missed this one as I was on hol.
As far as the electrical installation is concerned they are both TN-S.
Both cables look to be PILC which cannot be used to supply a PME supply to a customer. As has been commented cable work in the street may have converted it to PME, possible but very very rare within the constraints of PME and the network design has to be taken into account. (I've never known it to occur as we have access to 4c cables to use in PILC networks)
We work to very strictly laid down scenarios to cover these situations!
Oh and
1/
Nope, not legal and would earn whoever did that loss of authorisation and a serious interview with senior operations staff.
2/
We can only supply a TN-S earth from a non-PME system
We can only supply a TNC-S earth from a PME system
There is no interchangeability
As far as the electrical installation is concerned they are both TN-S.
Both cables look to be PILC which cannot be used to supply a PME supply to a customer. As has been commented cable work in the street may have converted it to PME, possible but very very rare within the constraints of PME and the network design has to be taken into account. (I've never known it to occur as we have access to 4c cables to use in PILC networks)
We work to very strictly laid down scenarios to cover these situations!
Oh and
1/
Looks like they've took a few strands of the neutral part of the concentric cable for the earth. To my mind that would make the neutral undersize at the cut-out.
Nope, not legal and would earn whoever did that loss of authorisation and a serious interview with senior operations staff.
2/
We can only supply a TN-S earth from a non-PME system
We can only supply a TNC-S earth from a PME system
There is no interchangeability