that is an issue but one that can be mitigated, the big problem with using service pipes for the main earth is the risk of them being replaced with plastic.homespark said:However, is the danger not from the low PFC?
The PE PFC is yes, the PN PSCC is much higher.At 14 ohms Zs on his ring, the PFC is 16A
direct human contact won't achive anything like that current anyway.which means (correct me if I'm wrong) that in the event of an earth fault (exposed metalic part becoming live or human in direct contact), the maximum fault current would be 16A
exposed metalic part becoming live you are correct about.
indeedwhich would not trip his 32A protection device for that circuit
that is what the main RCD is for, it will trip out on the small earth fault currents typically seen in a TT install.causing potential fire or electrocution. So how does that work for a TT installation with even higher resistance?