Yep, and fair enough.There is no gas pipe to the bugalow, just water and oil. The water pipe is plastic and the oil pipe is copper and just goes to my own oil tank about 10m away for heating purposes. The oil pipe is earthed as normal where it enters the bungalow and is run in a protective ducting as well as being plastic coated. I don't expect that the copper of this oil feed to ever touch ground and therefore should not accidently make an intended TT system to be TNC-S. ... Does that make sense so far?
That's you're decision - but it's perhaps worth pointing out that there are obviously millions of TN--C-S installations out there whose owners are not even aware of the potential issue, let alone done anything about it.I am more convinced now that I need to use one or more earth rods to provide an earth if the incomming TN is broken.
For a start, it's incredibly improbable that an earth fault in your installation would arise at the very same time as you had 'lost the TN neutral'. However, even in the event of that almost unbelievable co-incidence, it's not really the operation of RCDs/RCBOs (under fault conditions) that you need to worry about, since that only requires an earth impedance under about 7,667 Ω, which it would be very difficult NOT to achieve with any sort of earth rod (2" nail? ).At the moment I am thinking about using a number of earth rods to connect to the incomming TN connection. That way I get a fairly low earth impedance (to be measured and I would be surprised if it was anywhere near 0.35-ohm), which in normal operation will provide a good fault path under fault conditions to ensure that the RCBO's trip etc. .... Any ideas on what a good target earth rod impedance should be would be appreciated.
There's nothing wrong with your arithmetic, but I don't see that as a problem. If you had an incoming metal water pipe (and bonded it, as required), it's impedance to earth could be very much lower than 100 Ω, hence the continuous current very much above 100 mA, without your being able to do anything about that.... so I should be able to get a fairly low impedance. But I don't want it to be too low since the incomming TN connection may vary relative to true ground (depending on my loading and other users loading) which could mean a continuous earth current would flow through my earth rods. If for example TN was say 10V above true ground and the earth rod impedance was 100-ohm, this would be a current of 100mA continuously.
All true, but you would probably be aiming for an earth electrode of much lower impedance than 100 Ω, in which case the current under such fault conditions would be much higher than 2.4A. Indeed, if the earth impedance got anywhere near the 0.35 Ω, then that would represent an 'adequate' return path to the transformer, in which case your installation would function as 'normal', with all of what would normally be 'neutral current' flowing through the earth rod(s)!!Of coarse, if TN was losted, TN could be 240V (presumably) with an earth rod current of 2.4A.
Kind Regards, John