HI, I can understand its difficult to know what is going on without actually seeing it for yourself,Unfortunately I cannot upload pictures, The best way i can describe it, The extra sounders are supplied from the separate power supply (installed next to main panel), The bell and strobe triggers for these sounders are connected to the normally open on the relay contacts respectively, There are two relays, one for the sounders and the other for the strobe, The negative from the power supply is looped through the commons on the relays, This just leave the relay input trigger coil, the positive supply is coming from the psu, and negative supply is coming from the bell and strobe respectively from the panel.It's difficult to say what is going on from what you describe. You would normally only need to use relays if you're going over the switching current capacity of the panel output (most bell/strobe outputs will have a maximum rating, usually around 500ma)
Using relays, I would be connecting the 12v supply to the relay to the panel 12v supply, then the 0v supply to the relay to which ever output you want to trigger that particular relay (bell output for instance)
Then, you would use the aux power supply to feed whatever you want (additional sounders etc), switching the negatives of these sounders via the N/O of the relay contact. Connect the relay common contact to the 0v on the aux power supply and you have totally isolated it from the control panel, so that the panel is powering the relays and the power supply is powering the sounders.
The trigger relays are installed inside the power supply
Hope this is clearer.
thanks