Gas consumption was 7.425kwh (assuming 20 minute warm up), which means the system contents are ~ 140L (assuming cold at 25C)Hi
Thanks, so I kind of came up against 3 scenarios:
1. The boiler from cold getting up to temp (65ish) - 10988-454 up to 10989-129 - took around 20 mins
This gives a boiler output of 9.24kw which sounds more like it for the UFH heating.2. Boiler with just UFH on, wasnt making much noise, just seemed to be keeping temp - 10989-133 up to 10989-175 - 3 mins
If this again was over a 3 min period then the boiler output was 13.93kw, sounds OK with both UFH & DHW heating on although the water heating at ~ 13.93-9.24, 4.7kw seems a bit on the low side but not a problem really.3. Boiler with UFH on, and then the hot water kicked in (which is fed off the same heating circuit), sounded like it was working a bit harder - 10989-560 up to 10989-632
I did notice that when the hot water kicked in, the manifold temps went down by around 5-8 degrees, and didnt really recover properly until it went off, which may imply the hot water pump is pulling too much flow, meaning the return temps from the UFH are lower during that period and the boiler has to heat the return more?
The boiler pushes the water a short distance to a pipe that has the two manifolds, hot water, and rads for the top floor (never on), each of these has a pump, all are old CP53 on their lowest setting, and the hot water one is an evosta2, which is set on 'regulation with constant curve' on 1. So could be the hot water pump is pulling more water than it 'needs' and causing the boiler to work harder than it needs to when its on?
Sorry, maybe gone down a rabbit hole here...
Ta
Paul
Gas consumption was 7.425kwh (assuming 20 minute warm up), which means the system contents are ~ 140L (assuming cold at 25C)
This gives a boiler output of 9.24kw which sounds more like it for the UFH heating.
If this again was over a 3 min period then the boiler output was 13.93kw, sounds OK with both UFH & DHW heating on although the water heating at ~ 13.93-9.24, 4.7kw seems a bit on the low side but not a problem really.
Two data points that may help:Hi
Thanks for the reply, the manifold temps flow/return come up quite quickly, prob within 20 mins or so once it is on, so I dont think a massive amount of that time is spent heating really cold water. Currently my manifolds are at around 23 degrees, having been off for 2 hrs or so.
I currently pay 10.3p/kWh (the first ~500 are 15p), seems I am using quite a bit on average per year (~50000Kwh last 12 months), much of which I think was down to the bronze pump running constantly and my water tank then needed constantly reheated, which I fixed a few weeks ago
I suppose I want to get a feel for, if the boiler using that much over 6hrs is 'normal' or is that it really being pushed/is something else at play. It is condensing a decent amount (flow 65, return is around 42), but just seems like alot of gas to feed the 2 UFH manifolds, and top up the water tank after 2 showers.
Ta
Paul