@Johntheo5 – my big apologies, I should have been clearer that I was the one that set these.
D0: 12 – yes, 12K otherwise I find that when the burner fires, it heats up faster than it can modulate back down – so I get a burst of about 15 secs and then nothing until..
D2: 10 – because if I set it at 20 (default), I get a burst of heat (see D0) and then zip for 20 mins – and when you are trying to heat 4 UFH zones at about 40C, well, it never heats up of course..
D1: yes – I have it at 11 – so as to be sure that it covers the entire anti-cycling lockout, and I still get (residual) heat from the exchanger otherwise, not only do I not get any heat (see D0 and D2) I don’t get any flow either LOL!
D9: yes – exactly, so what is the V-Smart even thinking of to set this at 86 – when it is a UFH (profile AND a CH target hard set from the dial of 60C). It simply makes no sense to me, that V-Smart should call for 86C – unless I am missing something? (If V-Smart is disconnected, this number is sensible in the 40-50 range).
D17: yes, that’s my point, it works fine when set to 0 (default) BUT both Vaillant and a number of folk in this forum say that for UFH, it should be set to 1 (return) which kind of makes sense to be testing the return flow (low) temps from a UFH circuit – except that it just doesn’t seem to work if I set it for return – i.e. the boiler hardly ever fires, like there is no call for heat (but when there actually is of course).
D18: on this boiler, 0 is Return, 1 is non-stop and 2 is winter – with 0 as default.
D47: always shows 999 (whether V-Smart is connected or not) so I guess that 999 means no weather compensation – except, that I would expect V-Smart to identify itself as weather compensation surely?
D67: agreed – and my point about it rarely going over 5, indicates that D2: set at 10 (rather than 20) is probably sufficient, because anti-cycling time is naturally less than 10 in any case.
D19: default is 2, which means that speed is dependent on part load in D0 and as D0 is below 60% of the full load, then pump speed is 1, otherwise speed 2) . Setting to 0, means that heating pump speed is permanently 2 – but why this has suddenly become a requirement (in order to get heat to the upstairs rads in the last two weeks) is beyond me…