You probably will need the water at 45 degrees going into the floor with 40 coming back to the manifold.
The valve appears to be set to 50.
If the flow and returns to the manifold are at 60 or so, then the blending valve is guffed.
You cod try temporarily removing the capillary probe from the manifold above the pump and see if that helps.
The valve appears to be set to 50.
If the flow and returns to the manifold are at 60 or so, then the blending valve is guffed.
You cod try temporarily removing the capillary probe from the manifold above the pump and see if that helps.