All domestic boilers now are both condensing AND modulating!
Are they?
Heat pumps aren't modulating though.
Heat pumps are not boilers but heat sources.
But the better new inverter controlled heat pumps are variable output so they do modulate.
All domestic boilers now are both condensing AND modulating!
Are they?
Heat pumps aren't modulating though.
Heat pumps are not boilers but heat sources.
you cant give good advice if your knowledge is restricted to one product.You may question my motives if you wish, but they are to offer good sound advice.
Heat pumps are not boilers but heat sources.
My point was that, if you have a systrm with an ON/OFF heat pump, you may need a thermal store to avoid frequent starts under part-load conditions.
Quite, you don't want heats pumps frequently starting and stopping or the COP falls through the floor.
then there are thermal stores that run at very high temperatures to produce hot water...there is no real design rational to these other than they by pass G3 regulations...
Below the lowest kW rating a boiler will cycle on directly connected UFH. Most are 6kW minimum. Geminox make a boiler that modulates from 0.9 Kw to 10 kW. Ideal for direct UFH connecting most homes. For DHW use a large Intergas combi as a multi-point as it is reliable having few controls..
Have simple, cheap. zone vales for the UFH zones and stat-programmers on each zone. No weather compensation needed. Have a pipe stat set to 50C to protect the plastic UFH pipes. Set Geminox to approx 40-45C.
Below the lowest kW rating a boiler will cycle on directly connected UFH. Most are 6kW minimum. Geminox make a boiler that modulates from 0.9 Kw to 10 kW. Ideal for direct UFH connecting most homes. For DHW use a large Intergas combi as a multi-point as it is reliable having few controls..
Dr. Drivel (aka Water Systems, etc., ) I presume?
You could reduce the cycling on part load with a thermal store. Your proposal involves the use of 2 boilers, a Geminox for UFH and the Intergas for DHW. You could achieve the same with a secondary mixing valve.
well improve it....
Two combis, multi-point water heater, stratification, drivel, drivel, drivel, etc.,
Below the lowest kW rating a boiler will cycle on directly connected UFH. Most are 6kW minimum. Geminox make a boiler that modulates from 0.9 Kw to 10 kW. Ideal for direct UFH connecting most homes. For DHW use a large Intergas combi as a multi-point as it is reliable having few controls.
Have simple, cheap. zone vales for the UFH zones and stat-programmers on each zone. No weather compensation needed. Have a pipe stat set to 50C to protect the plastic UFH pipes. Set Geminox to approx 40-45C.
Do the costings. They all add up. Large thermal stores are not cheap. It is also simple and easy to connect up, and takes up far less space.
Below the lowest kW rating a boiler will cycle on directly connected UFH. Most are 6kW minimum. Geminox make a boiler that modulates from 0.9 Kw to 10 kW. Ideal for direct UFH connecting most homes. For DHW use a large Intergas combi as a multi-point as it is reliable having few controls.
Have simple, cheap. zone vales for the UFH zones and stat-programmers on each zone. No weather compensation needed. Have a pipe stat set to 50C to protect the plastic UFH pipes. Set Geminox to approx 40-45C.
Do the costings. They all add up. Large thermal stores are not cheap. It is also simple and easy to connect up, and takes up far less space.
I have radiators upstairs drivel what happens to the theory/drivel now.