Almost a year ago I was trying to resolve a few issues with our underfloor - see orignal thread in plumbing here:
https://www.diynot.com/diy/threads/underfloor-heating-a-couple-of-issues.493454/
The meachancal side is fairly under control (!) now nut the control side - electrically, is still having some issues.
Heating is UFH throughout property, on both floors.
There are two manifolds, one on ground floor, one on first floor.
Two wiring centers, and one controller.
Read more: https://www.diynot.com/diy/threads/underfloor-heating-a-couple-of-issues.493454/#ixzz5WGyCB4ao
The summarise the discussion from the other thread:
I noted that despite the room stats all having turned off, and rooms all being at temperature, the downstairs (as far as I knew) pump was still running. Since I had left the pump on setting 3 downstairs I was able to hear it (see mechanical issues i was having and why i had turned it up). I double checked and all stats required turning up to get a click, so they were all off at idle (room temp was satisfied). This should mean downstairs system should not circulate as I understand.
I set the controller to off, then back to auto, and the pump did not then come back on, unless I bumped any of the thermostats upward, as expected.
The stats for each floor seem to all correctly turn on their respective actuators, I checked this last year.
If I knock off all stats upstairs and downstairs, when both pumps were running, the pair both knocked off. But then only bringing a downstairs one back turns both pumps back on. It's not possible as far as I can tell to bring the upstairs pump on by itself. So i think that if upstairs stat calls for heat, but none downstairs is, then we cant get heat upstairs by itself, unless downstairs has been on and goes off, at which point, upstairs and downstairs pump stays on.
There is a wiring diagram that I dug out of docs on house, but despite it having two wiring centres, it only shows one pump.... So I don't know how that transfers to my system? I do have two wiring centres, but I have two manifolds and two pumps. I'll upload it shortly
I know pump had power, (since its been turned up to three and is louder) , it was resonating the wall again, so I can hear it in most of the house, even if it is faintly...
I have attached pdf of the wiring diagram I found and a jpeg. PDF is better quality - as I say, I don't know if its as installed, and I don't know how they handled the second pump, this diagram shows only one pump.
When looking at invisible heats manual, they don't have any system diagrams with two of their manifolds featured, so they never describe a system where zoning a manifold is required - HOWEVER, they do show two port valves in relation to systems with a hot water tank or similar, or radiators and underfloor , so I guess this is similar to having a second manifold.
wiring centre image:
4 white wires are actuators, two go to one block as they are driven from one stat in living room.
black cable is pump.
three grey cables furthest right are stats as far as I can tell.
Nothing seems loose or no signs of blown components, at least on this side....
The discussion turned to the relationship between controller and zone valves, or between 4 wire actuators and zone valves - which as far as I can tell, I do not have (zone valves that is).
I feels like somehow the wiring of the pumps and relays is incorrect.
Can someone help me please, as right now I must be wasting electrical and heat energy through circulating when i do no want to.
PDF copy of marked wiring diagram is attached in addition to the jpeg - the pdf can be zoomed once open for better clarity.
Read more: https://www.diynot.com/diy/threads/underfloor-heating-a-couple-of-issues.493454/page-2#ixzz5WGtzEK00
https://www.diynot.com/diy/threads/underfloor-heating-a-couple-of-issues.493454/
The meachancal side is fairly under control (!) now nut the control side - electrically, is still having some issues.
Heating is UFH throughout property, on both floors.
There are two manifolds, one on ground floor, one on first floor.
Two wiring centers, and one controller.
Read more: https://www.diynot.com/diy/threads/underfloor-heating-a-couple-of-issues.493454/#ixzz5WGyCB4ao
The summarise the discussion from the other thread:
I noted that despite the room stats all having turned off, and rooms all being at temperature, the downstairs (as far as I knew) pump was still running. Since I had left the pump on setting 3 downstairs I was able to hear it (see mechanical issues i was having and why i had turned it up). I double checked and all stats required turning up to get a click, so they were all off at idle (room temp was satisfied). This should mean downstairs system should not circulate as I understand.
I set the controller to off, then back to auto, and the pump did not then come back on, unless I bumped any of the thermostats upward, as expected.
The stats for each floor seem to all correctly turn on their respective actuators, I checked this last year.
If I knock off all stats upstairs and downstairs, when both pumps were running, the pair both knocked off. But then only bringing a downstairs one back turns both pumps back on. It's not possible as far as I can tell to bring the upstairs pump on by itself. So i think that if upstairs stat calls for heat, but none downstairs is, then we cant get heat upstairs by itself, unless downstairs has been on and goes off, at which point, upstairs and downstairs pump stays on.
There is a wiring diagram that I dug out of docs on house, but despite it having two wiring centres, it only shows one pump.... So I don't know how that transfers to my system? I do have two wiring centres, but I have two manifolds and two pumps. I'll upload it shortly
I know pump had power, (since its been turned up to three and is louder) , it was resonating the wall again, so I can hear it in most of the house, even if it is faintly...
I have attached pdf of the wiring diagram I found and a jpeg. PDF is better quality - as I say, I don't know if its as installed, and I don't know how they handled the second pump, this diagram shows only one pump.
When looking at invisible heats manual, they don't have any system diagrams with two of their manifolds featured, so they never describe a system where zoning a manifold is required - HOWEVER, they do show two port valves in relation to systems with a hot water tank or similar, or radiators and underfloor , so I guess this is similar to having a second manifold.
wiring centre image:
4 white wires are actuators, two go to one block as they are driven from one stat in living room.
black cable is pump.
three grey cables furthest right are stats as far as I can tell.
Nothing seems loose or no signs of blown components, at least on this side....
The discussion turned to the relationship between controller and zone valves, or between 4 wire actuators and zone valves - which as far as I can tell, I do not have (zone valves that is).
I feels like somehow the wiring of the pumps and relays is incorrect.
Can someone help me please, as right now I must be wasting electrical and heat energy through circulating when i do no want to.
PDF copy of marked wiring diagram is attached in addition to the jpeg - the pdf can be zoomed once open for better clarity.
Read more: https://www.diynot.com/diy/threads/underfloor-heating-a-couple-of-issues.493454/page-2#ixzz5WGtzEK00